Discuss Intended departure from the Regs in the UK Electrical Forum area at ElectriciansForums.net

happysteve

-
Esteemed
Arms
Supporter
Reaction score
2,115
As the designer of an installation, anyone put their name against an intended departure from the Regs (120.3)? If so, and you're willing to share, what were the circumstances?

Just wondering how common/rare this is.

Cheers! :)
 
I've done one:

DSC_0176 copy.jpg

Does not comply with 521.5.1 (ferromagnetic enclosures: electromagnetic effects). Earthing conductor enters steel enclosure separate from supply. PEFC <10A (TT; Ra ~30Ω; nothing extraneous), upstream OCPD 20A BS EN 60898 type B: no risk of EM effects.

~tin hat on~
 
I've done one:

View attachment 38611
Does not comply with 521.5.1 (ferromagnetic enclosures: electromagnetic effects). Earthing conductor enters steel enclosure separate from supply. PEFC <10A (TT; Ra ~30Ω; nothing extraneous), upstream OCPD 20A BS EN 60898 type B: no risk of EM effects.

~tin hat on~
Haven't got my BYB to hand but I'm sure reg 521.5.1 permits the use of a separate protective conductor to be run in parallel with an SWA cable.
 
It does. (Good memory!) The provision is for an additional protective conductor in parallel with the armour of SWA to enter the enclosure separate from the SWA. The earthing conductor is not in parallel. The armour is earthed only in the installation containing the OCPD (which is TN-C-S).
 
Agree with Lee - I think this arrangement may fall into the last para of that reg "It is permitted for such an additional conductor to enter the enclosure individually".
And, if I read the reg slightly differently, the SWA armour is the "appropriate protective conductor" for that circuit, and if it enters it should enter with the lives. But the earthing conductor for the TT installation is a different item altogether from the supply circuit protective conductor and so it may enter where it needs. Or is that stretching ?
Good looking job HS !
 
Departure from the regs is not as uncommon as may be thought from a deliberate intent perspective, the regulations are a guidelines and not law enforced although if you do digress from them you need to know your stuff and the materials your using down to the manufactures limitations. The BS7671 is a broad guideline and is suited to most in the industry and gives them somewhat a protective shield if ever the need should arise but it can not account for all the circumstances and situations out there, if you can ensure and provide a risk assessment for a departure from the regs that safety is not impaired and material used are adequate for their use and environment then it is acceptable to digress from the BS7671.
Doing it without reflecting on your position or considering the consequences if things go wrong is where you have to realise that you tread a fine line when departing from said regulations.
 
As goes the above query then you are not understanding how eddie currents work in metal enclosures, the earth will be strapped down to the enclosure if it was metal regardless where it enters, it becomes and issues not in domestic but at 100amp load plus where you take polyphase through separate holes, technically the regs apply across the board but the issue at domestic level are rarely of any practical concern.
 

Reply to Intended departure from the Regs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Sticky
A recent thread on the suitability of a cable supplied preinstalled on a manufactured floodlight/pump had me wondering a few things. Over the...
Replies
4
Views
895
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
849
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
885
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Hi all, Just wondering what the general situation is with other people on smaller jobs, do you give a quote or estimate to the client before you...
Replies
6
Views
988

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock