lee mcgregor

Right where do i begin ...

Got called to job because door had been kick in by police abd the door strike wasnt working so took off old strike and replace with exact same strike but new. New strike 8-12vac on testing i was getting 11.34v so that was fine . So after install door strike worked for say a week , then although it was still buzzing when someone push release at handset it wasnt releasing door .. thought might be faulty door strike so change it again for another new one . after a week it did the same , any ideas ???
 
as the door has been kicked in,is it the same door? if a new ones been fitted is it sitting right.if the door lock is pushing against the strike it wont release,if you can hear the strike buzz or click on pressing handset id say the door is pushing against it,try it with the door open and see if it works that way.
 
Right where do i begin ...

Got called to job because door had been kick in by police abd the door strike wasnt working so took off old strike and replace with exact same strike but new. New strike 8-12vac on testing i was getting 11.34v so that was fine . So after install door strike worked for say a week , then although it was still buzzing when someone push release at handset it wasnt releasing door .. thought might be faulty door strike so change it again for another new one . after a week it did the same , any ideas ???

Did you fit a MOV across the terminals?

Either that or you've got a possible short somewhere
 
Fail secure . the Strange thing was all i did was replace for an exact replica ... and the fact it works for some time first then decides not to is frying my brain.
 
As alarm man has said it'll be to do with mounting of the new door. There is no rime or reason why an identical door realise will not work with the existing install, something will be pressing on the latch, well I hope so good luck cheers good night. I love this diminished responsibility whilst posting technique.
 
Fail secure . the Strange thing was all i did was replace for an exact replica ... and the fact it works for some time first then decides not to is frying my brain.

has the lock failed or is it an intermittant fault,you need to do more tests,does it work with the rte button and breakglass or is it just the handset at fault,try it again with the door open and just use your finger to open it when button pressed if it works try pressing the latch back with your finger and press the release button if it works still that should rule out a badly fiiting door,if it doesnt it points to the door forcing on the latch,then start on the power tests,volts/current draw etc..
 
Ill be hoonest if you add to what the other guys have said , if the door was kicked in then the integrety of the wiring could be the problem if i were you id rewire that area as alarm man said its an intermittent fault so only way to be sure is to rewire ,weve all seen how the police kick in doors just a thought
 

Reply to intercom door strike problems in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock