Discuss Interesting read...loop testing and LED Dimmers in the UK Electrical Forum area at ElectriciansForums.net

Useful article.

Might be nice to start a thread in the Trainee forum for posting articles on various anomolies encountered during different test proceedures. This one would be a good one to open with. I'll see if I can find some articles on MOV's in switch mode supplies having an effect on IR test results and capacitive and inductive coupling causing ghost voltage readings on redundant cables to start with as well.
 
Possibly obvious to many but it's the kinda thing that probably doesn't get covered thoroughly in a classroom nowadays so I'm sure it would be of benefit to some as well.

Dimmers especially seem to cause confusion, the voltage waveform from a dimmer can also give weird readings on testers as well because of its rapid rise and decay and often altered phase angle.
 
Carry on this train of thought and you get to the realisation that dimmers affect the behaviour of the circuit under fault conditions. A fault downstream of a dimmer will probably not cause operation of the ocpd within 0.4S as a result of the current limiting effects of the dimmer.
Maybe a minor concern with the standard switch plate dimmer.
But what about a centrally located dimmer system? Will the ocpd operate in the required time on a fault between dimmer and load?
 
Useful article.

Might be nice to start a thread in the Trainee forum for posting articles on various anomolies encountered during different test proceedures. This one would be a good one to open with. I'll see if I can find some articles on MOV's in switch mode supplies having an effect on IR test results and capacitive and inductive coupling causing ghost voltage readings on redundant cables to start with as well.
yeah that would be a good thread for the trainee section. I'm back on Monday so could start it then as struggle on the phone unless you want to start it in the mean time ;-)
 
Carry on this train of thought and you get to the realisation that dimmers affect the behaviour of the circuit under fault conditions. A fault downstream of a dimmer will probably not cause operation of the ocpd within 0.4S as a result of the current limiting effects of the dimmer.
Maybe a minor concern with the standard switch plate dimmer.
But what about a centrally located dimmer system? Will the ocpd operate in the required time on a fault between dimmer and load?
Your standard dimmer will not restrict fault current as the triac should fail to the close position allowing fault current to pass.
 
this may not be what everyone does & only as we undertake a bit of new build work, we use click connectors or similar & we don't install lamps until after ZS same with Dimmers wago out or stick a temporary switch on, finish testing & then install lamps & dimmers. also helps with cash flow fitting a click & not having an expensive down light on the site that might be fitted for 40 days or so before final testing.
someone did mention to me a few years ago carry out r1&r2 & then calculate ZS which is fine but where possible we undertake ZS testing as part of our job.
 
Might be obvious to some, but it wasn't to me, when I encountered this issue last year. Installing some LED down lights, replacing old 12v ones. I had removed the old ones, and did my testing and got crazy Zs result. After lots of head scratching and dismantling the circuit, I removed the dimmer and got a decent Zs. Lesson learnt.

Wished I'd read that article sooner.
 

Reply to Interesting read...loop testing and LED Dimmers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
1
Views
247
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
649
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hello, I’m boarding out my loft for storage and I’d like some decent lighting up there rather than loft lights I’m currently using. I purchased...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock