Damsel in distress

Hi. I am trying to replace a 2 gang intermediate light switch. The switch I have currently has the following connections. Top: L1 and L1 on the left, Common on the right. Bottom: L2 and L2 on the left, L1 and L2 on the right. My new switch has the following. Top: L1 and L1 on the left with the same in the right. Bottom: L2 and L2 on the left with the same in the right. Some (not very clear) photos attached. Please can someone help me with the wiring.

image.jpeg

image.jpeg
 
The top pic is very unclear.
 
In the first picture the left hand switch is Intermediate, the right is 2 way

The new switch is 2 x intermediate switches.
On the left hand new switch match the connections on the old one. ie.
Top blue left, top yellow right
Bottom blue left, bottom yellow right.

On the righthand new switch put the Red that's in the old switch on the right into either of the new top righthand L1.
The bottom Yellow and Blue matching the old.

The righthand new Intemediate will work as a 2 way
 
In the first picture the left hand switch is Intermediate, the right is 2 way

The new switch is 2 x intermediate switches.
On the left hand new switch match the connections on the old one. ie.
Top blue left, top yellow right
Bottom blue left, bottom yellow right.

On the righthand new switch put the Red that's in the old switch on the right into either of the new top righthand L1.
The bottom Yellow and Blue matching the old.

The righthand new Intemediate will work as a 2 way

Thanks Snowhead I will try that now
 
Hi. I am trying to replace a 2 gang intermediate light switch. The switch I have currently has the following connections. Top: L1 and L1 on the left, Common on the right. Bottom: L2 and L2 on the left, L1 and L2 on the right. My new switch has the following. Top: L1 and L1 on the left with the same in the right. Bottom: L2 and L2 on the left with the same in the right. Some (not very clear) photos attached. Please can someone help me with the wiring.

View attachment 39114

View attachment 39115
Looks like the lef hand switch as you look at it from the back is an intermediate, whilst the right hand switch is a 2 way.
The replacement looks like a 2 gang intermediate, imo
 

Reply to Intermediate switch wiring in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I have a 220v House I want to change this switch to smart switch, but I am stumped, I don't have a neutral so I had to return the switch I...
Replies
2
Views
697
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
Hi I am trying to replace my old white light switches for nice chrome ones but the wires are all red but the new switch has only l1 l2 top and...
Replies
6
Views
689
Hello, I wish to replace the old 2 gang switch pictured, with the smart switch pictured. Am I right in thinking that all 3 reds wires would need...
Replies
0
Views
1K
our dimmer switch stopped working after 7 years so went to replace it at the weekend. When I opened it up, the black wire was in the common slot...
Replies
0
Views
229

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock