Discuss Internal wall insulation- help!! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all.

I am required to do a complete rewire on a 1920s terrace property with 9" solid brick walls which is then to be replastered using 30mm wallboards dot and dabbed to the brick- that is 18mm insulation backed onto a 12mm plasterboard.

Sure many of you have done this many times so my question may have an easy answer.

Do I surface mount the cables to the brick cutting the insulation off of the board in a channel around the cables and call it clipped direct? Don't really want to be uprating cable sizes and then derating them for insulation!

Obviously there is a direct conflict between keeping the walls warm and the cables cool!

Any advice would be appreciated immensely as the reference methods in the regs do not appear to cover this situation definitively.

Many thanks in advance
 
I would clip the cables to the wall and the thickness of the dab will mean you shouldn't have to cut away any of the insulation. You shouldn't need to de-rate the cables as the coolness of the brickwork and the airspace around the dabs will allow sufficient cooling.

Someone will be along shortly to disagree with me though!
 
I'll disagree with you :D
If I was clipping direct with insulation board going over the top I would probably calculate to method 102

Someone will be along shortly to disagree with me though!
 
25mm oval for 2 x 2.5mm cables in a drop.
 
hate capping. nails either bend on hard mortar or fall out of soft. drill and plug oval tube clips for me every time.
 
hate capping. nails either bend on hard mortar or fall out of soft. drill and plug oval tube clips for me every time.

Would there still be room for the boards to go over though Tel? The oval tubing is going to stick out more than capping.
 
If capping is specced on a job I always drill and plug anyway and drive the nails into the plugs. It saves a load of fannying on time.
As a rule I dont cap.
 
Ive never come across dot and dab for insulation backed plasterboard.

Will the adhesive stick to the foil?

Electrically as above no different to any other D&D plasterboard.
 
Ferg, not all insulated plaster board is foil backed mate. You can get stuff which has a layer of foam on the back, that's what's probably going on here.
Whether or not D&D adhesive will be any good for it is not our problem mate, that's for the boarders to sort out.
 
Ferg, not all insulated plaster board is foil backed mate. You can get stuff which has a layer of foam on the back, that's what's probably going on here.
Whether or not D&D adhesive will be any good for it is not our problem mate, that's for the boarders to sort out.

That makes sense.

Where I live, all external walls the plasterboard has to be foil backed.

Also d&d does'nt really exist as nearly everything is timber frame with block cladding.
 
Chase the wall use 20mm conduit and plaster it into the wall and if you or really paranoid you could use galvanized.It will take twice as long but in fifty years time it will be handy to rewire
 
Chase the wall use 20mm conduit and plaster it into the wall and if you or really paranoid you could use galvanized.It will take twice as long but in fifty years time it will be handy to rewire
So despite the readily availability of things like capping and oval conduit you'd really go to the trouble of all that work?
Don't forget, in 50 years time how many of the points that you put in are still going to be in the right place for the owners of the property then? So chances are you'll have gone to all that trouble for nowt.
 
To think why the trade is the way it is, the worlds full of twin and earth champions and dry wall liners this why the 50 mm rule was about 20 years late for all them poor handy and diy people got jobs wiring council and wimpy houses in th 70/80s.
 
How would you normally install behind dot and dabbed plasterboard?

Do that.

Thinking about it, you first need to establish what type of insulation is involved. If it's PUR or polystyrene insulation, then you'd need to cable the cable as the PVC sheath reacts with PUR and polystyrene insulation and the 2 shouldn't be in contact with each other.

If it's PIR insulation then I don't think that's an issue.
 

Reply to Internal wall insulation- help!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm currently refurbishing a room and in the process adding some internal wall insulation. The wall has been stripped and my electrician has...
Replies
5
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
233
Hi all, Our sparky has carried out first fix, twin and earth cables clipped to the block walls of our extension routed to each back box. His...
Replies
18
Views
5K
Just first fixed a house where I was initially told that the external walls were going to be battened then boarded, I used metal capping over the...
Replies
5
Views
1K
Hi I'm renovating a 1920s terrace and have stripped the lathe and plaster off a stud wall to an upstairs bedroom. I'm resurfacing the stud wall...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top