    Evening all, could someone enlighten me please as to what the function is of the small screen wire in an IS cable and where it should be terminated please. Bit short, but that's all really!!

    Cheers.
     
  2. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    Not sure what an IS cable is, but usually a screen is there to stop interference from electromatic and another sources.
    Usually the screen is connected to Earth at one end of the cable, usually at the origin or source.
     
  3. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    It is possibly the earth which is used to earth the IS equipment and is separated from the general electrical earth and is not there to carry fault current. Why do you ask because if those cables/circuits are incorrectly installed you could, depending on the environment asking be for serious trouble.
     
  4. Lagentium
    Offline

    Lagentium Regular EF Member

    Location:
    West Yorkshire
    I'm asking because I have to connect some at work Westy, I have my CompEx, but I've never worked on IS really, in fact, at all. I'm just being cautious really, I will see when I get the panel drawings tomorrow, it's been on my mind since I glanced down at the cable after I cut it today!!
     
  5. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Got you, I am no expert with these matters but I suspect if it is damaged it may require replacement.
     
  6. Rob
    Online

    Rob Trusted Advisor

    Location:
    North west
    Depends on what type of IS install it is. An what type of barriers are being used.

    It is most likely a drain wire for a shied, but where it connects its depended on how it is separated, either galvanic, optically etc...
     
  7. KennyKen
    Offline

    KennyKen Electrician's Arms

    Location:
    Australia
    Depends what instrincally safe instrument/component your terminating.
     
  8. Lagentium
    Offline

    Lagentium Regular EF Member

    Location:
    West Yorkshire
    The equipment is mainly pressure sensors and level switches. The pressure sensor is a Siemens product with a solenoid cap on basically. The drawings show me that the field end is made safe within the equipment rather than connected to earth and the other end in the panel goes to the IS earth, mounted below the barriers. Sound right? Don't bollock me Ken!
     
  9. Rob
    Online

    Rob Trusted Advisor

    Location:
    North west
    Sounds right, but confirm it with the designer.
     
  10. timbobelfast
    Offline

    timbobelfast Electrician's Arms

    Location:
    Belfast
    Normal 'IS' concept is that the screen floats in the field and is connected to earth in the safe areaat the barrier.

    Are Zener barriers being used?
     
  11. Lagentium
    Offline

    Lagentium Regular EF Member

    Location:
    West Yorkshire
    That tallies with the drawing Timbo, I shall look at the barriers tomorrow and report back, if I'm not too upset at missing the rugby!
     
  12. Cbuk2k2
    Offline

    Cbuk2k2 Active EF Member

    Location:
    Hull
    90% of instrument cables are supplied in 1 pair, 2 pair etc format because most instruments are loop powered (the 24v going to the instrument is also used to send the measured pressure etc). Each pair normally has a screen wire for noise immunity. If your running your instrument cables next to a power cable for instance. The screen should form a circuit all the way from the marshalling cabinet in the equipment room to the field. The drawing will tell you what to do in the field but in 99% of instances you tie it back with a bit of heat shrink or earth sleving over it. At the marshalling cabinet this should be connected to earth. If your using zener barriers (old stuff) you often find a dedicated IS earth in the panel which this should be tied to. With more modern galvanic isolators these are often tied to a clean earth.
     
  13. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    It should be terminated EXACTLY as the drawing says.

    No matter what anybody on here says or you think.

    That's is the golden rule of the concept.
     
  14. Cbuk2k2
    Offline

    Cbuk2k2 Active EF Member

    Location:
    Hull
    I'd say it was pretty poor practice to blindly folow any drawing.
     
  15. timbobelfast
    Offline

    timbobelfast Electrician's Arms

    Location:
    Belfast
    Not if the drawing is incorrect and you know it!

    Zenner barrier earths common with 'plant' earth instead of the 'clean' IS earth!

    As I have discovered after an instrument install was commissioned!
     
    • Like Like x 1
  16. LeeH
    Offline

    LeeH Insert witty monkey comment here. Electrician's Arms

    Location:
    Lincs
    If the drawing is incorrect then the drawing gets re issued.

    You do not deviate from the drawing.

    It's compex 101
     