Discuss IR test on lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
52
whilst carrying out EICR I usually find it near impossible to disconnect all loads ( on lighting especially) I there fore only carry out IR on Line and neutral to Earth.
However, when I see most other certs, they claim to have recieved 299 ohms on live to neutral?
Am I missing a trick, or am I just being honest . How do you guys get round this , or do you do as I do?
Thanks for any advice
 
Perhaps too honest. Calculate the time available to you to perform a EICR and you'll find that it is unlikely that you'll be given more that 4 hours to test and report on a standard 2-4 bedroom house.
Now ask yourself, what are the most important areas to test for to be assured that the electrical installation is safe to continue to be used.
Also, remember that its not to anybody's advantage to start disconnecting accessories which then have to be reconnected again.
Its usually sufficient to IR test between PE and L/N connected., polarity, EFL, and PFC, RCD, RCBO
 
The proformers are generally designed to be over complicated and get you to do unnecessary tests.. Notice that there is no mention of measuring the MPB but you might be expected to measure R1 and R2 of a final circuit which is unnecessary as you will check it when loop testing.
The best test instruments for basic anomalies are your eyes, ears, nose and touch..
 
So, as I thought, most folk are obviously not being honest on their forms, which then leads you to think what other false readings are they putting down?
Surely better to be honest ?
Thanks for the help , a lot of good people on this site .
 
To be honest mate if that is the only thing they lie on its not to bad. I was at my sister's before just on the computer with my nephew and her landlord sent a sparky round to do a eicr and he was there maby 40 minutes and it was suppose to be a 100% test and inspect and there was no way he tested every thing as he did not even come in the front room and the tele and xbox did not even turn off so he obviously didnt do dead test on the ring or test the rcd as the tele would of gone off.
 
To be honest mate if that is the only thing they lie on its not to bad. I was at my sister's before just on the computer with my nephew and her landlord sent a sparky round to do a eicr and he was there maby 40 minutes and it was suppose to be a 100% test and inspect and there was no way he tested every thing as he did not even come in the front room and the tele and xbox did not even turn off so he obviously didnt do dead test on the ring or test the rcd as the tele would of gone off.
40 mins!!!
It takes me 40 minutes to get set up and take the client details and readings from the supply!!!
My friend also had EICR done through a letting agent , 8 circuits , the guy was there an hour!
I'm either really slow, or too thorough, or maybe both!!
 
One method I've used is to switch off all the lights, test live neutral, live earth, and neutral earth, and then go round, switch the switches on, and test between live and earth again. When the circuit is looped through the light fittings, this seems to cover all the insulation to be tested.
 
The are generally designed to be over complicated and get you to do unnecessary tests.. Notice that there is no mention of measuring the MPB but you might be expected to measure R1 and R2 of a final circuit which is unnecessary as you will check it when loop testing.
The best test instruments for basic anomalies are your eyes, ears, nose and touch..
Deleted
 
its hard to guess at really, 1 bedroom flat i did yesterday had 13 circuits, alot of 1 beds ive done have been 4 or 5 circuits

could also be a storage heater board which can be a pain if its not marked properly

just do as you do, l/n - e , then l - e , if both pass then all 3 outcomes have been covered
 
The proformers are generally designed to be over complicated and get you to do unnecessary tests.. Notice that there is no mention of measuring the MPB but you might be expected to measure R1 and R2 of a final circuit which is unnecessary as you will check it when loop testing.
The best test instruments for basic anomalies are your eyes, ears, nose and touch..
How are you proving R1 +R2 100% when you are doing a loop test?
 

Reply to IR test on lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
636
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
644
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
612
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
838
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
327

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock