Hi all,
Testing question for you.
I'm currently testing an existing domestic installation. The wiring is about 20-25 years old.
We have rewired some of the older circuits and added newer circuits too. During my insulation resistance test, over two-thirds of my results were coming out at 500MOhms. These circuits had new cabling and older cabling on them.
I know its unusual to get such high (perfect readings) like that, so my question is, would the fact that I'm testing through older cables with newer cables bring the IR reading up? The only other circuits that are lower than the 500 are circuits with only the older cabling on them. I have switches on for lighting circuits, no loads connected that would alter results
Any advice would be greatly appreciated.
Testing question for you.
I'm currently testing an existing domestic installation. The wiring is about 20-25 years old.
We have rewired some of the older circuits and added newer circuits too. During my insulation resistance test, over two-thirds of my results were coming out at 500MOhms. These circuits had new cabling and older cabling on them.
I know its unusual to get such high (perfect readings) like that, so my question is, would the fact that I'm testing through older cables with newer cables bring the IR reading up? The only other circuits that are lower than the 500 are circuits with only the older cabling on them. I have switches on for lighting circuits, no loads connected that would alter results