Discuss IR testing MICC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

Bradzz

Hi all
my problem is when IR testing MICC the readings keep droping to 00M ohms:sad_smile: i have 29 circuits to test in a large building, and the circuits i have so far tested have all been 00M Ohms ? could any one offer me some advice please. Bare 2L 1.5mm MICC.
icon3.png
Any other problems i might come accross would be most appricated:D.

Cheers people
icon14.png
 
When finished with the IR test earth the conductors you just tested to disapate the charge as MICC acts like a capicitor when testing
 
Hi all
my problem is when IR testing MICC the readings keep droping to 00M ohms:sad_smile: i have 29 circuits to test in a large building, and the circuits i have so far tested have all been 00M Ohms ? could any one offer me some advice please. Bare 2L 1.5mm MICC.
icon3.png
Any other problems i might come accross would be most appricated:D.

Cheers people
icon14.png

Well that's obviously not right is it, so you must have connected loads on these circuits you've tested. What's the values your getting for L-E/N-E?? Really need a lot more information, before anyone can give you guidance...


 
Hi all
At the DB i disconnect Phase Nuetral linked them together for the lighting circuits, then test to outer of MICC.
also i have tryed P-N/P-E/N-E all the same 00, My brain is hurting as i cant understand why this is happening on all circuits inc socket outlets.
some circuits show a value then just drop off to 00 the tester bleeps each cycle, the time it gets to the second beep this is about every 1 to 2 seconds is down to 00.
Light switches in both positions. i have also broken down some of the circuits and using a wonder lead checked i have the correct Phase and Nuetral.
any other infomation you may require to give me some advice jsut ask.

Thanks all for your help cheers people. and for the quick replies.
 
is the tester okay? have you pressed the button without connecting it to anything at all to see if it is faulty?
 
Tester is all good new batts put in the same day, also checked againts my check box. Will take 2 more testers with me.
re checked today all good.
 

Reply to IR testing MICC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
642
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
679
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
876
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
712
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
378

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock