Any ideas gratefully received.
I'm testing a new ground floor extension. Brand new lighting circuit. Live switches. Only feeding jcc fgled6. Continuity is fine. 0.33 at furthest point. Circuit disconnected from the cu I've had readings from 88MOhms to >299MOhms line/cpc. The others are fine. Being <1Mohm I became paranoid and began testing each leg. Each leg comes back >299MOhms but when I start bunching the cpcs into the terminal or croc clipped IR reading begins to drop off. It's wired in 1mm with 22 downlights the load being 1.8amps if they're all on. Ceiling void is insulated celotex and cable clipped direct or capped and in plaster. Multiple two way and intermediate switches.
It's not too hot today 23 degrees ambient but reasonably humid as tiling has been laying the large floor space.
Any ideas as I want to go home now!
I'm testing a new ground floor extension. Brand new lighting circuit. Live switches. Only feeding jcc fgled6. Continuity is fine. 0.33 at furthest point. Circuit disconnected from the cu I've had readings from 88MOhms to >299MOhms line/cpc. The others are fine. Being <1Mohm I became paranoid and began testing each leg. Each leg comes back >299MOhms but when I start bunching the cpcs into the terminal or croc clipped IR reading begins to drop off. It's wired in 1mm with 22 downlights the load being 1.8amps if they're all on. Ceiling void is insulated celotex and cable clipped direct or capped and in plaster. Multiple two way and intermediate switches.
It's not too hot today 23 degrees ambient but reasonably humid as tiling has been laying the large floor space.
Any ideas as I want to go home now!