Discuss Is a seperate FCU required for spur? in the UK Electrical Forum area at ElectriciansForums.net

MicMcG

-
Reaction score
0
Hi all,

I am looking to add 2 spurs off a ring main socket and the 1st is a 3 gang socket with a 13A fuse (see pic). The 2nd will be 2 gang. Will I still require a seperate FCU or will the 3 gang socket fuse cover this requirement? I beleive it will but just want confirmation. Thanks.
 

Attachments

  • ae235.jpg
    6.1 KB · Views: 8
The fuse in the 3g socket protects the third socket, this is a workaround to satisfy British standards.

The fuse doesn't protect outgoing cables.

So if these new sockets are all to be connected to the same spur then they would all need to be connected via a 13A FCU or SFCU.
 
The fuse in the 3g socket protects the third socket, this is a workaround to satisfy British standards.

The fuse doesn't protect outgoing cables.

So if these new sockets are all to be connected to the same spur then they would all need to be connected via a 13A FCU or SFCU.

I thought this may be the case too. I found it on Screwfix and on the Q&A section a member of staff replied that the 13A fuse protects all 3 gangs MK Logic Plus 13A 3-Gang DP Switched Plug Socket White - https://www.NoLinkingToThis/p/mk-logic-plus-13a-3-gang-dp-switched-plug-socket-white/17315#product_additional_details_container

To play it safe I'll just stick an FCU in.
 
I thought this may be the case too. I found it on Screwfix and on the Q&A section a member of staff replied that the 13A fuse protects all 3 gangs MK Logic Plus 13A 3-Gang DP Switched Plug Socket White - https://www.NoLinkingToThis/p/mk-logic-plus-13a-3-gang-dp-switched-plug-socket-white/17315#product_additional_details_container

To play it safe I'll just stick an FCU in.

I have just checked and indeed it does protect all 3 outlets, but that doesn't change anything as far as spurs go.
If you are putting 2x points on a spur from a ring then it needs to be a fused spur.

You are only permitted one point on an unused spur, the triple socket is one point, a twin socket is one point.
 
I thought this may be the case too. I found it on Screwfix and on the Q&A section a member of staff replied that the 13A fuse protects all 3 gangs MK Logic Plus 13A 3-Gang DP Switched Plug Socket White - https://www.NoLinkingToThis/p/mk-logic-plus-13a-3-gang-dp-switched-plug-socket-white/17315#product_additional_details_container
I have just checked and indeed it does protect all 3 outlets, but that doesn't change anything as far as spurs go.
If you are putting 2x points on a spur from a ring then it needs to be a fused spur.

You are only permitted one point on an unused spur, the triple socket is one point, a twin socket is one point.

Thanks for all your help Dave, much appreciated. I'll grab an FCU for it.
 
Just for information I found the above Interesting, in the latest update of the French regulations a three gang socket counts as three points etc, it was a significant change as being all radial circuits for power outlets the maximum of 12 sockets on a 2.5mm circuit and 8 sockets on a 1.5mm circuit suddenly lots of installations do not comply with the latest Regulations, not that they are retrospective of course.
 
Just for information I found the above Interesting, in the latest update of the French regulations a three gang socket counts as three points etc.
Given the lack of fused plugs, etc, in that system it seems a massive oversight not to count each connectible point individually in the first place!

But lets keep the ring/radial/etc debate to the threads for that topic!
 

Reply to Is a seperate FCU required for spur? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
765
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
750
Hi, apologies for the basic question In a radial circuit, is it permissable to spur off the supply side of an existing fused connection unit...
Replies
1
Views
455
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi all, Thank you in advance... So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to...
Replies
17
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock