Discuss Is it OK to connect a PIR in parallel with a wall switch? in the DIY Electrical Advice area at ElectriciansForums.net

Andy_C

DIY
Reaction score
2
Hi, I want to add a PIR to a porch light but I want the original light switch to still behave as it always has.
i.e. both the light switch and the PIR can switch on the light.
The diagram shows what I want to do. The circuit is pretty simple and will work as I want. My question is this... Is it correct/safe to connect the switch and PIR in parallel like this?
Thanks!Switch+PIR 2.jpg
 
no problem with that,, however you will need to take a neutral cable to the pir as well
 
no problem with that,, however you will need to take a neutral cable to the pir as well
Great, thanks James.
I was thinking that when both switches are on it would create a loop in the live supply which might be a problem. So you reckon the loop is ok and isn't bad practice or anything?
Yes, I was thinking that about the neutral to the PIR 👍🏻
 
assuming the lives are from the same source (same breaker and therefore the same phase) not an issue.
 
assuming the lives are from the same source (same breaker and therefore the same phase) not an issue.
The live for the PIR will come from the supply side of the original light switch, so yes both lives are from the same breaker âś…
Thanks again James, much appreciated.
 
Many lights that come with sensors can longer be opened up to find the switch wire from sensor to light.
As such, they gave a switch sequence to bring the light on permanently… ie, turn it off-on-off- on within 3 seconds

No extra switch required
 

Reply to Is it OK to connect a PIR in parallel with a wall switch? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi there, I have an outside light that is turned on with a switch from inside and would like to change it to a PIR version incorporating an...
Replies
8
Views
1K
I needed to illuminate our dark side walk at the house. I have used two PIRs wired in parallel which switch four LED lights. The idea is no matter...
Replies
10
Views
2K
I have a single wall switch powering 1 light and I want to add a separate light and change to wall switch to a double to power them both...
Replies
4
Views
378
Hi, I have a single light switch, wired like this.. the 2 wires in com, with a always live wire coming to the switch, and then wire going out to...
Replies
6
Views
687
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock