Is Part 'P' enforceable?

Discuss Is Part 'P' enforceable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Bob Geldoff1234

-
Esteemed
Arms
Reaction score
768
I recently wired an extension for a customer and certified it and notified Part'P' Building control so all good.
As I was working on this extension the neighbour from across the street came in to have a nosey.
Anyway the upshot is the builder is building an extension for the neighbour at the moment.When speaking to the builder I thought I might get the job of wiring his extension but evidently the neighbour himself is wiring it.He is not a qualified electrician and doesn't belong to any scheme.I have told the builder that he cannot wire his own extension without getting the council to certify it and inspect it at all the stages.This,he has not done.
So my question is,when the building inspector asks for the part 'P' certificate he obviously cannot give one.Is the house owner breaking the law? Could the council make him rip it out? If they accept an EICR instead then it makes a mockery of Part 'p'?
What is everyone's thoughts on this?
 
He won't get a Completion Certificate from building control without proof the electrical work is compliant.
It'll just sit with Building Control as not yet complete and he won't be able to sell it.
He'll have to go down the "Electrician has disappeared and not notified it" route.
 
If there is full plans approval then as far as I know the electrical inspections are paid as part of that fee

when the building inspector asks for the part 'P' certificate

In my experience all he will ever expect is a installation certificate ! He would then take no action to check from whence it came but would go away happy that his responsibilities have been discharged

If they accept an EICR instead then it makes a mockery of Part 'p'
Part P needed no one to make it a mockery that was self evident from the outset

Could the council make him rip it out
Theoretically yes they can,but realistically no,they would do all they can to get someone to accept responsibility for the installation
 
A lot of domestic electrical works are not under part p ie minor works (ie extending an existing circuit)
Also if LABC do not pass off works then when time to sell up they can buy planning permission indemnity insurance, which in some cases is so much cheaper then doing it the right way
 
The last building inspector I spoke to wanted me to send him the Part 'P' certificate directly to him so he could sign it off.He said waiting for the NIC's notification from them took a few weeks delay.He never asked to see the installation certificate!.
It really gets my goat that I have to jump through all different hoops to be qualified and safe and yet no one gets in trouble when jokers like this do their own work.I despair:(
 
I was registered 2 days ago and found during my time that competitors ( some of them mates)they had no problems at all after doing notifiable work whilst not registered

Registration is also a voluntary means of complying
Because someone is not registered it does not mean they are not qualified or are a cowboy installer
Its a personal and business decision whether to register,it has never been compulsory,maybe that is why it was all doomed from the outset many years ago,its likely only us doers of "what should be" are at all concerned and in hindsight we were always the mugs who did it right
 
just to make a note......some building inspectors dont know what they are asking for either.
I had job where a engineer spec'ed a steel RSJ but i could not carry out the work until the LABC had those calculations checked by a out sourced company. i asked the inspector about her qualifications and she had none related to building, engineering etc etc so they had to double check things !!!
What a waste of money
 
The last building inspector I spoke to wanted me to send him the Part 'P' certificate directly to him so he could sign it off.He said waiting for the NIC's notification from them took a few weeks delay.He never asked to see the installation certificate!.
It really gets my goat that I have to jump through all different hoops to be qualified and safe and yet no one gets in trouble when jokers like this do their own work.I despair:(
Bob had he done that in the US and the local code enforcement found out he would be took to court and probably fined him $ 500.00 plus the state would get their state investigator to go out and investigate the job himself and yes he can have it took loose. Then charge him for that service of doing it over.
 
Ashrow, I had the same scenario. The architect specified an RSJ, but correctly farmed it out to a structural engineer to give the exact spec.
The builder (and i use that term loosely) was in the process of installing the RSJ when the architect turned up, measured it and rejected it. The builder simply shrugged, said he had it in store and it would do the job. BC arrived and the lad said he had no experience so had to go with the structural engineers spec.
The new one arrived 3 days later, and it was massively bigger...all the builder said was it had cost him £80.
Had the architect not been on hand, half an hour later the RSJ would have been in place, covered over, and no-one would have known any better....until the Grand Piano fell through the floor into the garage below!
 
Building control is a joke. I saw a post on a facebook group saying that where notifiable work is done, one labc tells builders to get an electrician to certify the work after its done, knowing that no electrician was involved in the installation
 
Bob had he done that in the US and the local code enforcement found out he would be took to court and probably fined him $ 500.00 plus the state would get their state investigator to go out and investigate the job himself and yes he can have it took loose. Then charge him for that service of doing it over.
1567452757514.png lol. :D four bleating words
 
Bob had he done that in the US and the local code enforcement found out he would be took to court and probably fined him $ 500.00 plus the state would get their state investigator to go out and investigate the job himself and yes he can have it took loose. Then charge him for that service of doing it over.

Sounds a better way to deal with things that.
 
I remember a few years ago when finished a new building ,gets a call its the building inspector have got your member number and test cert number not even finished the job .
[automerge]1567453272[/automerge]
I was registered 2 days ago
wow ,try since 2005 john fat watch me belly punch out presctot ,love the guy
 
Surely the government has "Part P" detector vans? They have them for the TV licence job....can't see no reason for not extending the foolishness xxxx i mean,policy...:)
 
A lot of domestic electrical works are not under part p ie minor works (ie extending an existing circuit)
Also if LABC do not pass off works then when time to sell up they can buy planning permission indemnity insurance, which in some cases is so much cheaper then doing it the right way

A friend of my brother (in Norwich) had this exact scenario, had ‘Martin’ from down the pub wire he’s 2 storey extension 5 years ago never notified LABC or issued an EIC, sold his house in July, indemnity insurance cost him £50, LABC fee was over £200 5 years ago.
 
I was registered 2 days ago and found during my time that competitors ( some of them mates)they had no problems at all after doing notifiable work whilst not registered

Registration is also a voluntary means of complying
Because someone is not registered it does not mean they are not qualified or are a cowboy installer
Its a personal and business decision whether to register,it has never been compulsory,maybe that is why it was all doomed from the outset many years ago,its likely only us doers of "what should be" are at all concerned and in hindsight we were always the mugs who did it right
Des
Allthough in essance i agree with you that there are too many chancers and jokers out there that can and do carry out ---- work. there are also a lot of very good electricians that are not registered due to the fact they are employed by a company that is registered as such do installations to a very good and safe standard but only do domestic works for freinds/family or even in there own property yet are not allowed to fill in a test cirtificate from their registered company due to fact that company has not done invoicable work on the property and because the clowns at the councils are just pen pushers with tick boxes to wok off its is sometimes like talking to a brick wall not to mention they just see an opertunity to dip the owners pockets for money.
Oh the arguments i have have with thickos its all good fun especially when they try telling me that a 2 miniute Part P qualified numpty is going to have to inspect a 30 year qualified electrical engineer with test and inspection 16th, 17th & 18th edition SAP qualified and HND in electrical engineering's work. Me thinks not.
 
The last building inspector I spoke to wanted me to send him the Part 'P' certificate directly to him so he could sign it off.He said waiting for the NIC's notification from them took a few weeks delay.He never asked to see the installation certificate!.
It really gets my goat that I have to jump through all different hoops to be qualified and safe and yet no one gets in trouble when jokers like this do their own work.I despair:(
Welcome to modern Britain !
 
Having been asked recently by some old customers and their conveyancing solicitors for copies of electrical certs & compliances certificates they forgot to store in a safe place, I kinda feel they are catching on to this thing now.

I boring myself repeating this, but I moved house last year. You are required to fill and sign a legal document, stating, amongst other things, if you've had any electrical work carried out since 2005.

If you research indemnity insurance, some suggest its not worth the money. It only indemnifies you against legal action by your LBC, but not for poor workmanship (there's a time limit on regularisation for prosecution or enforcement). And who wants to buy a property thats a bag or worms, so to speak.
 
. And who wants to buy a property thats a bag or worms, so to speak
A certificate or a notification is no guarantee of anything. My friend bought a brand new house two years ago. All NHBC, part P, FENSA, signed off by LABC.
Two years later he is still battling for about a dozen issues to be fixed.
 
Bob had he done that in the US and the local code enforcement found out he would be took to court and probably fined him $ 500.00 plus the state would get their state investigator to go out and investigate the job himself and yes he can have it took loose. Then charge him for that service of doing it over.
I love the American legal system. We really need to sit up and take notice.

Maybe once we are out of the shackles of Europe we could get shackled with America as the 51st state.
[automerge]1568912208[/automerge]
Having been asked recently by some old customers and their conveyancing solicitors for copies of electrical certs & compliances certificates they forgot to store in a safe place, I kinda feel they are catching on to this thing now.

I boring myself repeating this, but I moved house last year. You are required to fill and sign a legal document, stating, amongst other things, if you've had any electrical work carried out since 2005.

If you research indemnity insurance, some suggest its not worth the money. It only indemnifies you against legal action by your LBC, but not for poor workmanship (there's a time limit on regularisation for prosecution or enforcement). And who wants to buy a property thats a bag or worms, so to speak.
I’ve been asked a lot more than I ever have also. I think your right.
 
Des
Allthough in essance i agree with you that there are too many chancers and jokers out there that can and do carry out ---- work. there are also a lot of very good electricians that are not registered due to the fact they are employed by a company that is registered as such do installations to a very good and safe standard but only do domestic works for freinds/family or even in there own property yet are not allowed to fill in a test cirtificate from their registered company due to fact that company has not done invoicable work on the property and because the clowns at the councils are just pen pushers with tick boxes to wok off its is sometimes like talking to a brick wall not to mention they just see an opertunity to dip the owners pockets for money.
Oh the arguments i have have with thickos its all good fun especially when they try telling me that a 2 miniute Part P qualified numpty is going to have to inspect a 30 year qualified electrical engineer with test and inspection 16th, 17th & 18th edition SAP qualified and HND in electrical engineering's work. Me thinks not.
Phewf.….I've just come up for air after trying to read the 'sentences'. I agree with the lines of your post, especially the last paragraph...but the bad spelling and lack of commas and full stops left me out of breath.;)
 
almost me. 30+ years, 16th, 17th, HND. can't be arsed to jump another hoop (18th), college ain't got access for my zimmer frame.

Gees. I’ve been in the business 29 years. If you count the 4 year apprenticeship started at 16.... was out the business, back in... out, in out... shook it all about!

16th, 17th and 18th... and an unused BSc

I’ve done a few jobs where LABC have been involved and only one asked for my gold card. (No P up here)
I think that was more my customer being an argumentative t**ser and the council making him do everything to the letter.
 
It’s all good and well the householder taking out indemnity insurance against a whoever did the dodgy electrical work.....but I’d imagine the insurers will certainly be chasing the installer should the worst happen,
 
part pee is a joke. at the time, it was a golden opportunity to make all electrical work ( excepting simple accessory swaps DIY) only to be carried out by qualified sparks, similar to the gas safe register, but apparently there was not enough clout brought to bear by the trade and insufficient income for the scams and the likes of b&q, who sell electrical equipment to any punter with the cash , to make this work. a case of a horse designed by a useless committee and the result being a a camel.
 

Reply to Is Part 'P' enforceable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top