Mr. Anderson

I've just looked at a job in a residential home where I need to replace a sfcu. The circuit is on a old cu and I've noticed that the main earthing is in 6mm and has thermal damage, I've quoted to also upgrade this. My question is the cu is on a SP TN-S and has 3 cu coming direct off the supply (3 main earting conductors). It's impractical (but not impossible) to disconnect power to all consumer unit to take a Ze reading, would you guys take the Ze reading for the one consumer unit with all parallel paths from the other cu connected (not a true reading), remove the power to the other cu so you can remove the main earthing to those cu (wont take long and is safe but is going to cause problems for all at the house) or remove all parallel paths from the other cu whist keeping the power to them on (not safe)? P.S. It might just be my computer but I cant seem to drop down a line to start a new paragraph?
 
Hard one to judge without being there as it were. You need to discuss it with whoever is in charge at the residential home, as you may find that you can isolate the whole install for a short period during the day.

If you cant isolate the supply to all 3 DBs, then all you can do is a Zdb at each board. Don't remove the earthing conductor from the MET while any of the boards are powered up for obvious reasons.
 
I'm sure you need a single point of isolation for the whole installation, so if you can negotiate a short shutdown, you could get one in and get your Ze.
With the added advantage of some extra work! :)
 
Depends what you define as an "installation". Its possible imo to say in this instance that there are 3No installations, each with their own integral main switch located within each DB. I think this is acceptable as long as each switch is labeled as such.
 

Reply to Isolating power to mutpil CU for Ze in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
702
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock