Discuss Joists in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Ross1

-
Reaction score
16
I am familiar with the regs on a new build 25% and 40% of the joist span is for your cable holes (hope im right there) In an extension though do the same rules apply cause I'm in a situation where I need to drill within the first 10% of the span for a shower cable.Cheers
 
isnt the rule for drilling any joist 0.125 * the height of the joist, think its in the electricians guide to the building regs and also the on site guide, this gives the maximum sized hole to drill
 
the buildings regs are clear that on all buildings "part A" should be applied as it is statutory
holes are 0.25 to 0.40
notches are 0.07 to 0.25
nothing in the middler
 
How come then a plumber will come along after you have got boards up and whack great big notches above where you have carefully drilled your holes central in the joist happened quite a few times to me lately they don't give a flying f..... to the building regs
 
How come then a plumber will come along after you have got boards up and whack great big notches above where you have carefully drilled your holes central in the joist happened quite a few times to me lately they don't give a flying f..... to the building regs

they should nt but of course they do
 
THATS why I love old miners cottages (for example!) - no mucking about in them days with joists, just chuck a tree in. Drill away it'll support a skyscraper
 
How come then a plumber will come along after you have got boards up and whack great big notches above where you have carefully drilled your holes central in the joist happened quite a few times to me lately they don't give a flying f..... to the building regs

Because their pipes go in the notches, hold up the floorboards, and have more than enough strength to maintain the building's integrity ;)

pj
 
I think drilling any holes or chopping of slots in the twig like joists they use today in house building, will seriously affect them. Unlike the sizes of joists used in yester-years, when it was rare to see less than 6 X 2'' joists, many being twice that width!!
 

Reply to Joists in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Most of the work I do is additions and alterations in domestic properties, and other than swapping accessories and lights in new-builds for...
Replies
2
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock