Discuss Just how smart are "Smart Meters"? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening
classes; I haven't learned much since. Intro over..................HELP!
I live in a bungalow with electricity as the only energy supply. This supplied via an RTS and economy 7 meter an old 6 way consumer unit for normal household loads and (via the RTS) to a 4 way consumer unit dedicated to night storage heaters (approximate total load of 10kW). Under duress (discontinuation of RTS) I agreed to having an Economy 7, 5 wire Smart Meter installed, where the 5th wire controls the "off peak" load switching. OK, everything normal, took him 4 1/2 hours to install but we have all had jobs like that have we not?
I changed supplier but kept record of meter reading twice a day (22.00, bedtime and 08.00 pre breakfast time). I soon started to realise that I was clocking 5 kWh on the Day time tariff every NIGHT. The Night time tariff increased as expected. I switched off 1 mcb of the "normal" consumer unit
each night but the 5 units remained constant. Started timing checks and found that the LOAD csu switches ON at 00.07 BUT the NIGHT tariff switches ON at 00.33 (times are aprox) and as old Faraday said "10kW over 30 mins equals 5 Units. The supplier will not listen to any argument. Complaint is escalating but they stick to the mantra that they are allowed to be 2 hours out of sinc. and I am out of pocket £325 per heating season.
Any ideas for next step?
 
Interesting what you say, I have allowed with my system for the change to be half hour out, so start charging at 0:30 and stop at 7:30 but night rate should be I am told 0 to 8. My heating is oil, so yesterday my use was Power used 6th March as example.jpgwhich is normally less than £3 a day total. It does not seem I have any method to hard wire any change over from using battery to charging battery, seems I am on EV charging tariff however I don't have an EV unless counting my ebike.

Since a fixed change over time no real need for telemetry, I am with British Gas, and Octopus I am told do cheaper rates, but they vary, both time an tariff so simple timer will not really work.

As with you on switch on at in my case 0:30 I use most of the power going to be used that day, in my case by 2:00 the battery is nearly fully charged, so I could delay switch on until a lot latter, and although I have a dip in the morning it does not go low enough to mean I import.

However we have had economy 7 for years, think it started in the 80's, but then we got economy 10 which had a boost during the day, and now a whole host of tariffs, I am still trying to get pay in payment sorted, but once done, money may go in and out of bank account for electric but it will near enough be net zero.

You can't hope to get to that, but a delay unit at least for some of the storage heaters could help.
 

Reply to Just how smart are "Smart Meters"? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
557
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
937
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock