Hi,
If you're a spark, you're reading this, your name is Kevin, you work in the Manchester area and you did a job in Rusholme yesterday on lights that kept tripping the RCD - Please reconsider your career before you do serious damage.
It's forgivable that you were unable to diagnose an insulation fault with the lights and blamed it on a faulty RCD (though the customer said you thought it was both RCDs which should have made you think again). I presume you don't have the right equipment for insulation & RCD testing?
It's also forgivable taking the lights off the RCD as a tempary measure.
What isn't forgivable is taking the 1.5mm lighting circuit with an insulation fault on it, taking it off the 6A breaker and putting it directly on the main ccu switch protected only by the suppliers 100A fuse! To compound matters you didn't even put it on the consumer side. Instead putting it on the supply side so when the customer was getting a firework display last night - they couldn't even isolate the electrics!!!
I don't know how much current was going through the light fitting but even the copper had disintergrated.
I seriously believe if I hadn't attended at 1am this morning there wouldn't be a house still standing.
 
I'd like to like this post but it seems strangely wrong to attach a like to something so serious.
it's good that there are still sparks out there responding to dangerous situations like the one in caveman's post. my hat off to OP for going out @ 1.00 a.m. and saving the situation.
 
Get him reported before he kills himself or someone else, the customer must have his details, even if it was a cash job they must have a mobile for him which should be passed on to the authorities.
Did you get any pics for evidence.
 
Well i suspect if somebody else phoned the cowboy and said they want some work doing he would appear like the cat in Alice in wonderland.

I would send rogue traders on the watchdog/BBC a link as they love a good story like this one. i would also contact local papers and name and shame him that way. He needs stopping. In this area last year trading standards got an injunction against a 'plumber come heating engineer' who was lucky not to have killed people when working on boilers. he is now not allowed to do such work as part of the court order.
 

Reply to Kevin please change careers before killing someone in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K
Hi All, I was wondering if anyone could help me with a recent problem I’ve had on a job. About 5 months ago I installed about 5 outdoor soffit...
Replies
12
Views
5K
Hi, Before I begin my tale of woe, I have my tin hat ready! I'm retired from the trade, I started out just as the 16th came in and had a rather...
Replies
35
Views
4K
Hi Don’t often post on here but I’ve dreamt about this issue last night. Need advice please Yesterday I attended a property to complete an EICR...
Replies
9
Views
1K
Toneyz
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock