Search the forum,

Discuss L&N-E IR Test (and we still haven't fixed the stupid 20 characters) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

hightower

When you do a L&N-E IR test, is there anything (other than a fault) that could be left plugged in that would produce a low reading?
 
surge protection?
I'm not asking for a particular scenario, like I'm not having issues. Just wondering if there's any predicament that could cause a L&N-E IR test to cause a low reading and stick that knowledge in the back of my head somewhere.

I guess with surge protection, it would show on a 500V test but wouldn't show (or show to the same degree) on a 250V test?

Anything else?
 
IT equipment. computers are renown for having small earth leakage.typically around 3mA apiece. that's why you never put too many on a circuit with RCD protection.
 
IT equipment. computers are renown for having small earth leakage.typically around 3mA apiece. that's why you never put too many on a circuit with RCD protection.

See what I'm trying to understand is that the regs says it's okay to tie L&N together and test to earth when vulnerable equipment is on the circuit - so what would be the point of that if they give false results
 
I had a socket outlet RCD in a RFC give me low readings. Likewise a shaver point.
 

Reply to L&N-E IR Test (and we still haven't fixed the stupid 20 characters) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
665
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
704
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
744
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
523
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock