Search for tools and product advice,

Discuss L&N-E IR Test (and we still haven't fixed the stupid 20 characters) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

hightower

When you do a L&N-E IR test, is there anything (other than a fault) that could be left plugged in that would produce a low reading?
 
surge protection?
I'm not asking for a particular scenario, like I'm not having issues. Just wondering if there's any predicament that could cause a L&N-E IR test to cause a low reading and stick that knowledge in the back of my head somewhere.

I guess with surge protection, it would show on a 500V test but wouldn't show (or show to the same degree) on a 250V test?

Anything else?
 
IT equipment. computers are renown for having small earth leakage.typically around 3mA apiece. that's why you never put too many on a circuit with RCD protection.
 
IT equipment. computers are renown for having small earth leakage.typically around 3mA apiece. that's why you never put too many on a circuit with RCD protection.

See what I'm trying to understand is that the regs says it's okay to tie L&N together and test to earth when vulnerable equipment is on the circuit - so what would be the point of that if they give false results
 
I had a socket outlet RCD in a RFC give me low readings. Likewise a shaver point.
 
Well no, it's not necessarily a way of cutting corners. The regs describe the test, but my question is what benefit does it bring if the results are still going to be influenced by equipment
 
OK, the scenario where I'd imagine using this is not for an EIC but maybe to do a quick global IR to make sure an RCD will hold - obviously this will then have a full test but I'm thinking just a quick way to find out if it should generally be OK
 
Because the results are most likely going to be worse than if you split test with all loads disconnected. Thus if it passes with results that are going to be pulled down by equipment it stands to reason that the circuit is serviceable and without loads, be in better standing.
 
Its a handy method for EICRs when you either cant disconnect everything, or are unsure of any loads that are connected without your knowledge.
 
( Is it a reason to start splitting ring up ... or is that cheating )
Localise !
Never mind IT equipment plenty of naff IEC cables out there !
(IEC leads may test good at 120V for some reason ...)
 
Last edited:
There is an argument,for "cutting corners",there is also an argument,for including additional sections of an installation,within a test.
We could have that discussion for an eternity...

The actual required tests,are of the installation alone,and not any additional parts,accessible or not. If this is not possible or practical,obvious allowances and measures,are required,to obviate this.

All that is really important,is for all testing,to be relevant and fully understood.
 
( Is it a reason to start splitting ring up ... or is that cheating )
Localise !
Never mind IT equipment plenty of naff IEC cables out there !
(IEC leads may test good at 120V for some reason ...)
IT equipment should not give false readings unless they incorporate filters and this is rare. IEC leads should never give false readings. Testing an office last night nothing unplugged all circuits above 100 meg. Shaver socket is a new one on me and I think you need to ask if such things and IEC leads give false readings then they are faulty.
 
I wasn't able to examine the shaver TX it had been installed under a floor that had then been laminated. There was no FCU it had been tapped into the RFC.
Apparently the Unit has its own internal fuse but of course if that did blow you need to rip the floor up to replace.
Anyway upshot was low IR readings with it in circuit. Disconnected RFC from both sides of it and the rest of the ring read fine. Had to "assume" the TX has some sort of filtering to earth. Had been working fine for years and worked fine on new RCBO for that RFC and has done since.
 
The shaver point on the wall was just passive. The feed to it is the SELV from the TX.
The advantage is the shaver point is small with nothing in it and no in separated mains is fed near it. They aren't very common.
 
The shaver point on the wall was just passive. The feed to it is the SELV from the TX.
The advantage is the shaver point is small with nothing in it and no in separated mains is fed near it. They aren't very common.
How do you know it provided an isolated supply.
 
It's not a test i would carry out with anything plugged in, i would aldo disconnect lamps and Led lights and smoke alarms. It's the only way you'll ever be 100 confident in it results
Pointless exercise unless you get odd readings.
 

Reply to L&N-E IR Test (and we still haven't fixed the stupid 20 characters) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
650
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
694
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
733
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
513
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock