Search the forum,

Discuss Landlords EICR and t&e sub mains without RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Would there be much point putting a 100ma RCD upfront of one of these sub mains as it still wouldnt meet the 30ma requirement?

in my opinion it would be worth it, especially if it was me that had just put a nail through the cable.
 
For TT surely there must be some kind of RCD up front, as changing to SWA would be worse than useless - a nail connecting to a live wire and to a high Z earth that just makes the building live but trips nothing is worse than a nail on its own that is just live.
If you can beef up the thin bit of wall to 50mm, or maybe make the route un-hidden in some way (metal detector and some labels/paint ? ) then a 100mA or 300mA up front would be my preferred But a long run of any cable on TT without an upfront RCD is asking for trouble, even a few m of meter tail in plastic trunking feels icky.
 
For TT surely there must be some kind of RCD up front, as changing to SWA would be worse than useless - a nail connecting to a live wire and to a high Z earth that just makes the building live but trips nothing is worse than a nail on its own that is just live.
If you can beef up the thin bit of wall to 50mm, or maybe make the route un-hidden in some way (metal detector and some labels/paint ? ) then a 100mA or 300mA up front would be my preferred But a long run of any cable on TT without an upfront RCD is asking for trouble, even a few m of meter tail in plastic trunking feels icky.

An upfront RCD is not a must, although in most TT situations tt is highly likely. Especially in domestic situations where it is not only needed for fault protection due to low Zs.

I've done a few installations where the Ra is sufficient not to require them.
 

Reply to Landlords EICR and t&e sub mains without RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock