Can you supply a latching coil through it's own set of NC contacts? Or would it try to drop out as soon as it tries to pull in.
 
Last edited by a moderator:
You can only latch a relay on your using the n/o contact.

as you suggest, using n/c means it will turn off as soon as it turns on.
 
Thanks to everyone who responded.
It has been solved.
The relay in question was an Allen Bradley 700 PL400 A1 with an Mechanical attachment. Turns out the mechanical attachment was the problem.
Still curious how the relay is able to pull in before the series NC contact breaks.
 
Ive added a pic of the circuit
 

Attachments

  • A&B CKT.jpg
    21.7 KB · Views: 10

Reply to Latching relay chattering. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
591
Im trying to make a Star Wars Prop for a course project where the dealine is comming up very fast in days and I need to do the report so really...
Replies
0
Views
370
I previously posted about having a single phase reversing motor which I thought had a centrifugal switch. After looking into it more, it actually...
Replies
1
Views
1K
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
Replies
0
Views
479
Hi guys, A car showroom / workshop brand we do work for has asked us to modify a few things in the workshop. One of them being to implement...
Replies
7
Views
926

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock