Discuss LED downlight issue 1x keeps cutting out in the Lighting Forum area at ElectriciansForums.net

Reaction score
7
Can any one help?
Just been to a customers house and in a loft extension there are 6x LED downlights (cob). The last downlight in the circuit seemed to be cutting out when the dimmer was at the minimum so I replaced the standard LED for a varilight dimmer so the minimum could be adjusted slightly. Even after this, when the dimmer is switched off, adjusted to minimum and switched back on that one downlight in the circuit seems to stay off. Any ideas? Maybe volt drop?
 
Hi - maybe the lamp itself is a bit odd. If it was easy I'd try moving it and see if the fault moves to the new location ...
 
Hi, thanks for the reply i have tried this, they are the cob downlights with the fixed lamp but i still moved it to a different location and the same thing still happened at the end of line so it isnt a lamp issue by the looks of it, i could understand if it was 50 downlights but with just 6 i cant see why‍♂️
 
How many times have you adjusted the varilight dimmer? . Try adjusting the minimum until it doesn’t go wobbly!
After checking for poor connections first.
 
I checked for loose connections and all seemed fine, i spent a while setting up the varilight dimmer with different minimum brightnesses and also tried changing the “driver mode” on it, i set the minimum brightness just off the maximum so there was barely any dimming actually happening and the same still happened... turned the switch off and back on and that same one didnt kick in untill the dimmer was turned up slightly!
 
Think about it logically. Its always the last on the line that is at fault? And its not the fitting itself 'cos you've swapped them about.
Not a loose connection, you say you've checked.

It must be a damaged cable between last and second from last position.
Do you know which fitting is second from last? It might not be the one you expect.
Disconnect all the lights and check for continuity, and IR.

It all takes time, and it is up to the customer if they want to pay for it or just do without the last light.
 
If it is COB GU10 then you may have to try a different make at least to eliminate the lamps themselves.
I like @static zap idea of a ring or split radial but as the horse has bolted and decoration is final then other ideas are needed.
 
(Build a rig -independent of setup -to measure each lamp , check they all have near identical draw , keep the frugal , swap out any thirsty ones)
..They are sure to be near identical if you test them..(sods law)
 
Are the LED lamps and varilight dimmers 'compatible'? Sounds like a incompatibility issue if as you say all terminations are sound.
I've experienced similar and found it to be either down to programming of the dimmer or compatibility!
Cant imagine volt drop being an issue.
 

Reply to LED downlight issue 1x keeps cutting out in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
206
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
431
Hey all, hoping someone can help with a particularly annoying problem! Have changed a load of LED downlights to the fixed bulb Centorio type (14W...
Replies
2
Views
979
Done a job yesterday, remove old 12v halogens and replace with mains, gu10 downlights. Fitted some LED gu10's no issues. Got a call today saying...
Replies
9
Views
873
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
694

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock