Discuss LED strip ceiling lights in the Lighting Forum area at ElectriciansForums.net

Reaction score
0
Hello all.

I want to fit LED strip lights to the ceiling with 45 degree channeling and diffuser around my son’s room. As there are so many different types, brands, lengths, amps/volts, accessories etc I could use some advice from anyone who’s done this please and the most reliable site to order from.

1. Is it possible to join 4 lengths together with 90 degree connectors with only 1 power supply, or would I need 2? (The room has a perimeter of approx 15m).

2. Is it possible to buy a plain power cable extension that could run from the plug all the way up the corner of a room then the LED starts at the ceiling? (As opposed to having LEDs running up the corner of the wall?)

Any advice or guidance would be greatly appreciated. I have watched many YouTube videos but nothing is covering all bases for my specific needs.

Cheers guys,
Bazz


.
 
15m won’t be a problem. Most strips are sold as so many watts per metre…. Multiply by length to get total watts and get the power supply next size up.

Electrical wholesalers will be able to source everything including the aluminium mouldings and a cover strip.
 
Every LED strip has a maximum length before voltage drop is an issue and you will see visible dimming towards the end of the strip on a 15m strip
12v strips max is around 5 m and 24v strips is around 10 m

So I would recommend you buy 24v LED (with the correctly rated driver for at least 15m) and install the feed in the middle feeding 2 x 7.5m LED instead of 1 x 15m LED
 
Every LED strip has a maximum length before voltage drop is an issue and you will see visible dimming towards the end of the strip on a 15m strip
12v strips max is around 5 m and 24v strips is around 10 m

So I would recommend you buy 24v LED (with the correctly rated driver for at least 15m) and install the feed in the middle feeding 2 x 7.5m LED instead of 1 x 15m LED
Agreed. I bought three 5 metre LED strips to run from a USB supply. The spec said you could have 4 strips connected together. First strip fine, next strip dimmer third strip dimmer still. Solved it by effectively wiring the strips up as a ring (end strip cabled back to power source.)
 

Reply to LED strip ceiling lights in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I’m after some advice please. I’m installing some LED profile around a customers bedroom ceiling for some led strip to sit in and...
Replies
2
Views
536
As the title says. But then I cut off a jst connection off one of the light strips and I can't get them to work together... the one strip is plug...
Replies
1
Views
504
First time poster here seeking a little advice/confirmation I have spurred off to a fused switch and from there running two 2.5mm cables to the...
Replies
2
Views
714
Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock