First post all so go easy lads....
What's people's views on maximum amount of LEDS on a 6amp mcb lighting circuits?? 6w LED GU10s throughout. Wired in 1mm twin and earth. Maximum cable runs??? Nearly every spark I speak to has a different verdict. Should we still be considering if 50w halogens are to replace the LEDS on circuit design?? Practically everyone uses LEDS now.
As for cable runs/volt drop it would take roughly 38 6w lamps to pull an amp.
1 x 44 x 140=6160
6160/1000= 6.1 volts
A cable run of 140m with 38 LEDS on??
Do people consider this good practice???
Am I missing something???
Obviously if your r1/r2 ZS readings satisfactory.
What's people's views on maximum amount of LEDS on a 6amp mcb lighting circuits?? 6w LED GU10s throughout. Wired in 1mm twin and earth. Maximum cable runs??? Nearly every spark I speak to has a different verdict. Should we still be considering if 50w halogens are to replace the LEDS on circuit design?? Practically everyone uses LEDS now.