From what you describe it sounds like the installation should be TT or perhaps was TT but this is no longer the case. The submains supplying other buildings which require main protective bonding would require a cpc adequate to support PME bonding and for a swa cable it would have to be a 50.0, 4 core minimum to support 10.0 bonding. As to whether the entire site should be TT and there is a suspicion it may originally have been is not possible to say from a distance. Do you have a copy of GN7 to refer to.
 
It probably once was as the boards dont look very old so it has probably been faffed with, Would the 32A control panels be required to just have 1sec disconnection time on TT?as it would be simple enough to get 30mA protection to the conveyors circuit, but if not i guess id need to fit a30mA rcd within each control panel.
 
You need to complete the EICR and consider remedial ramifications after however I feel you are undertaking a task you may not be competent to do.
 
thanks, I did touch on that in my first loooooooong post
with reference to reg 705.411.1
(i) all circuits supplying socket outlets are indeed covered by 30mA RCD.
(iii) - which requires all other circuits are protected by a 300mA RCD, well they are covered by the 100mA type S, but is this acceptable? I genuinely do not know the answer to that question. - reg 705.422.7 says S type can be used but it does not say if that s also acceptable for ADS
 
Your 100mA time delay tripping times are 500ms max and 130ms min.
If it's protecting circuits with a 0.2 second disconnect time this maybe problematic depending on what the s type trips at.
with a 300mA rcd the max tripping time is 300ms and when testing the rcd needs to trip really below 200ms for a 0.2 disconnect time for circuits upto 32 amp.
 
The 100ma s type will provide a better level of fault protection. Have you decided if it is agricultural.
 
its, as you say agricultural by definition, and that does include processing facilities according to the definitions in the BYB.

the type S went out in 176ms but this is with it having 0.2 ze as it is at present, I cannot confirm how quickly it will operate if it is on TT.

The thing getting me in a tangle now is the discon times, in the agricultural section there is no mention of the 0.2/1sec times only the level of rcd protection, as post #16
 

Reply to levels of rcd protection on TT system - long post - prepare cuppa first! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
Evening all... I'm having a complete mind blank on what the mA requirement is for an RCD on domestic household with TT earthing, Ra = 57ohms. I'm...
Replies
47
Views
14K
Customer has a large metal caravan with three phase supply feeding 3 metal Consumer units with split load RCD outlets contained within - all...
Replies
18
Views
2K
....TN-S appears outside, butt TT employed inside. Good Evening Everybody (This is my first post) Overview: The supply to my parent's cottage...
Replies
29
Views
4K
I've just carried out a periodic inspection on a building on an old RAF/USAF site. Commercial single story building. Wiring system is around...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock