Discuss Life is a (British) Gas in the UK Electrical Forum area at ElectriciansForums.net

sparksburnout

-
Esteemed
Reaction score
1,766
Got a call from a local guy this week, said he is getting a fishy smell when using his shower. Went to have a look, had got 25mm tails from his main CU along with a pair of 6mm singles (with a few strands chopped off both tails) going to a separate Wylex 3036 jammed into the outgoing side of the old style analogue meter. The terminations at the meter were covered in a big black mess of charred insulation and the meter casing was in a right state. No main earth, no bonding, main CU also an old Wylex. Gave him a list of things to sort out, starting with a new meter from supplier (British Gas), followed by a visit from WPD for a PME and isolator so that his other problems could be addressed, advised that he forgot about the shower for the meantime.
BG then told him we have nobody available until next week. I told him to impress upon them it was a fire risk and needed doing urgently. So, guy from BG eventually drags his --- round, puts in new digital meter, connects outgoing tails into new henley blocks, terminates both CU's into them using existing tails and says "there you go pal, everything should be fine now"
Customer now thinks I am talking bullox and says "I will get back to you if I have any more problems". No main earth, no RCD to (newly connected) shower, no bonding. "Looking after your world"?? I don't think so.
 
And at the other end of the scale, a property I visited today has the card as below left with the householder
Notice from BG.jpg
And yet
Gas Bond.jpg
Their wording is out of date also.
Good old BG
 
DNO will look after the supply cable, cutout.
Energy supplier taking care of their meter and tails up to the henley block.
And from there is customers responsibility, including the earthing, rcd, etc...

dude swapping the meter may not be electrician at all, his job is to change the meters, thats it...
 
DNO will look after the supply cable, cutout.
Energy supplier taking care of their meter and tails up to the henley block.
And from there is customers responsibility, including the earthing, rcd, etc...

dude swapping the meter may not be electrician at all, his job is to change the meters, thats it...
I know that and agree with you, but the thing that annoyed me was the "Everything's OK now mate" comment made to the customer, more or less inferring that I was overdramatising things.
 
Got a call from a local guy this week, said he is getting a fishy smell when using his shower. Went to have a look, had got 25mm tails from his main CU along with a pair of 6mm singles (with a few strands chopped off both tails) going to a separate Wylex 3036 jammed into the outgoing side of the old style analogue meter. The terminations at the meter were covered in a big black mess of charred insulation and the meter casing was in a right state. No main earth, no bonding, main CU also an old Wylex. Gave him a list of things to sort out, starting with a new meter from supplier (British Gas), followed by a visit from WPD for a PME and isolator so that his other problems could be addressed, advised that he forgot about the shower for the meantime.
BG then told him we have nobody available until next week. I told him to impress upon them it was a fire risk and needed doing urgently. So, guy from BG eventually drags his --- round, puts in new digital meter, connects outgoing tails into new henley blocks, terminates both CU's into them using existing tails and says "there you go pal, everything should be fine now"
Customer now thinks I am talking bullox and says "I will get back to you if I have any more problems". No main earth, no RCD to (newly connected) shower, no bonding. "Looking after your world"?? I don't think so.

Did you charge him for the call out and advice?
 
Did you charge him for the call out and advice?
No I'm a soft dollop like that, probably should have done but I get loads of work via word of mouth in my smallish community and I think it benefits you in other ways sometimes. Guy was obviously not flush either. I just looked in on my way home he's literally down the road, took 5 mins. Would you?
 
No I'm a soft dollop like that, probably should have done but I get loads of work via word of mouth in my smallish community and I think it benefits you in other ways sometimes. Guy was obviously not flush either. I just looked in on my way home he's literally down the road, took 5 mins. Would you?

I'm no shining example in this area, I changed three light switches and a shower pull cord last week, I didn't charge for labour thinking that the friend would give me a drink, I ended up with £5! However I am a trainee and am just trying to
get a bit of experience under my belt!:)
 
I'm no shining example in this area, I changed three light switches and a shower pull cord last week, I didn't charge for labour thinking that the friend would give me a drink, I ended up with £5! However I am a trainee and am just trying to
get a bit of experience under my belt!:)
This is an important part of learning for a trainee. Jobs you do as a favour are invariably the jobs that turn out to be more involved than you first think plus they usually come back to haunt you one way or another. Also if you work for free once they expect it in future and gawd help you the day you actually try to give them a bill for something..
 
This is an important part of learning for a trainee. Jobs you do as a favour are invariably the jobs that turn out to be more involved than you first think plus they usually come back to haunt you one way or another. Also if you work for free once they expect it in future and gawd help you the day you actually try to give them a bill for something..

Noted!;-)
 
This is an important part of learning for a trainee. Jobs you do as a favour are invariably the jobs that turn out to be more involved than you first think plus they usually come back to haunt you one way or another. Also if you work for free once they expect it in future and gawd help you the day you actually try to give them a bill for something..

Particularly in a pub . or other small commercial premisses.
 

Reply to Life is a (British) Gas in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hello All Strange question for you, I know you don’t have crystal balls :) but can anyone give me any clue on the following… I have mid eighties...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock