Discuss Light switch wiring question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi. In regards to a 1way light switch that has a loop installed at the switch can I simply install a new switch and put the loop wires in l2 and the switch in l1?

384326A7-68E3-4FC4-8879-048367C61FA3.jpeg
 
Loop into top terminal and switch in L1. Connect the earth to the earth terminal of the switch as it requires a direct connection to earth.
 
Hi. In regards to a 1way light switch that has a loop installed at the switch can I simply install a new switch and put the loop wires in l2 and the switch in l1?
If you do that, it will not work, ever.

Where do the 'loop' wires terminate at the moment?
What colour are these 'loop' wires?
 
Some switches have a terminal marked ‘loop’ which is where the neutrals are connected to. This terminal has no function for the switch and is simply somewhere to park the neutral wires.

If your new switch doesn’t have this, use a bit of connector for the neutrals.

A photograph of the existing switch connections and all the cables at the switch would help us give you more accurate advice.
 
What you have there, is a 2 way switch.
Depending upon the switch position, you will have continuity between either L and L1 or L and L2.
If you were to put the permanent live into L and the neutrals into L2, whenever you switched off, your fuse or MCB would blow or trip. All your lights would go off.
You could feasibly put the permanent live into L1 and the neutrals into L2.
I would not recommend doing such though.
 
Neutrals into L2? But then what would happen??!!
 
Some people write replies without thinking of the consequences of what they are writing, this is part of being an electrician is you understand how all the component parts work, I read a post the other day, “on how do you do a rewire” crazy that we even reply to these people especially the general public.
 
Further to the comments “what you have there is a 2 way switch” all one gang switches that are enhanced, chrome, satin, etc are nearly always 1 gang 2 way, find out the facts first then you can give advice that fits the situations
 
Further to the comments “what you have there is a 2 way switch” all one gang switches that are enhanced, chrome, satin, etc are nearly always 1 gang 2 way, find out the facts first then you can give advice that fits the situations

It is a fact that the picture showed a 2 way switch. Not sure what you are getting at here?
 

Reply to Light switch wiring question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am trying to replace my old white light switches for nice chrome ones but the wires are all red but the new switch has only l1 l2 top and...
Replies
6
Views
688
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
603
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
325
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
548
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
849

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock