UK Lighting a Tennis Court

Discuss Lighting a Tennis Court in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I want to put 6 300w LED flood lights around a tennis court positioned centre and corners. The cable run is approx. 80 meters. I have a 1.5mm rubber external cable in free air mounted along the top of the mesh fence. 1800w at 240v should give me 7.5a which is within the cable rating but how do i account for voltage losses raising the current draw?
 
how do i account for voltage losses raising the current draw?

The maximum permissible voltage drop is a small fraction of the supply voltage. We used to say 3% for lighting to maintain the efficiency of filament lamps but with electronic LED drivers that could be relaxed somewhat, as the internal regulation maintains the light output and the efficiency of the fixtures themselves is nearly constant over modest voltage variations. But too high a voltage drop can cause the drivers to malfunction, and it also represents wasted energy (as heat) that appears on the electricity bill. Therefore it makes sense to limit it to say 5-6%, or perhaps 10% at the very worst.

For constant power, the current is inversely proportional to the voltage, so if the absolute worst case is 10% drop, then likewise the absolute worst case is 10% current increase. It's an approximation but there are too many contributing variables involved, including cable temperature, driver efficiency curve, etc, to be worth refining the maths at all.
 
Can someone explain where the 10A comes from, please...?
That would be my fault - rounding up 1800W to be 10A for the sake of easier maths in this thread. The real figure would be around 8.7ish
 

Reply to Lighting a Tennis Court in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock