For selecting the correct cable size how do I determine the cable length in a loop in lighting circuit? Will it be the distance from the consumer unit to the final ceiling rose? Do I have to take into account the cables running from each ceiling rose to the light switch? I have attached a simplified circuit diagram. I think the csa of the conductors and cpc will be 1 mm2 but i have to prove this in my calculations. This is part of a uni coursework so i'm only looking for some advice not for answers. Any input would be greatly appreciated. Not sure if i've posted in the correct section.

multi-point-radial-lighting-circuit1-590x544.jpg
 
Hi - think about the reason for the calc (i.e. what will set the limit and push you from 1 to 1.5 say. Is it current rating, is it voltage drop?). Then work out the worst case (longest path) path that current flows and this will give you the length you need for the calc. Hope that helps a bit.
 
Your longest length of cable is the limiting factor that you need to take into account, the line conductor from the rose to switch and back adds to the length of the line conductor.
so consider a fault from switched line to earth in ceiling rose 3.
Also as an aid to calculation consider the switch to rose as a line earth or line neutral length then you can just measure total length of cable without having to break it down to line, neutral, earth. This would be slightly more onerous than reality due to the reduced csa earth in twin and earth but errs on the side of safety.
 

Reply to Lighting circuit cable selection in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
625
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
477
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
864
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
884
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
808

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock