just rewiring a down stairs lighting circuit its all wall lights had faults all over the place on the existing wiring so decided to rewire all apart from kitchen lights .
it was all wired in 1mm so have changed it to 1.5mm all circuits are in jb's
and i have sitting room lights dining room lights landing light and kitchen now the kitchen is still in the 1mm wiring .
At each jb have done a IR test on each circuit before connecting all togeather all fine however when i connect the sitting room lights i get a reading of around 800mohms .
yet take it off feed all ok checked the mains feed and that is ok.
I am stumped could it be the old cable (1mm) thats giving me silly results (bearing in mind tested on own its fine) i am kinda chasing a ghost ! any idears.
using a Metrel tester .
 
Can you be more specific with the IR readings, 800mOhms? do you mean 800 Ohms or 800 MOhms? Where? L-N, L-E, N-E?
 
Last edited by a moderator:
Does this tester go up to 1000 M ohms on a test an if so when he tests the whole cct connected together is it now dropping down to 800 as you won't get milli ohms readins with a IR tester.

1/RT = 1/r1+1/r2 etc lower result when tested as whole
 
Last edited:
800Megohms could be achieved by breathing on the leads!!!!
 
Things you need to let us know, what tester are you using, what are the I/R test results before connecting living room lights, P/N P/E E/N for each, and after connection, also what are your continuity readings, any reason for leaving the 1mm kitchen lighting circuit, did you wire the drop downs to the wall lights, and switches.
if you think the cable to the living room light might be damaged, i would change that section. We await your response.
 
Last edited by a moderator:
Its a metrel easy test i am getting >1000 IR on all tests on individual junction box connections i.e living room, landing lights sitting room and kitchen now i connect them all to mains feed (which is also >1000) and i am in the clear except when i connect the dining room lights , which on there own gives me >1000 but connected the whole circuit drops to around the 800's . I havnt done the kitchen because of access problems , even though it is comming up >1000 . I cant find a leak anywhere its a neutral earth problem , and as i said everything is new apart from kitchen, would the old 1mm cable to the kitchen be giving me hassle when loaded with the rest of the circuit??
Oh and all wiring has been changed 1.5 down to wall lights as well.
 
Last edited:
if you are getting 800meg. what are you worrying about. could be a tiny bit of leakage in a fitting. i certainly wouldn't lose any sleep over it.
 
Things you need to let us know, what tester are you using, what are the I/R test results before connecting living room lights, P/N P/E E/N for each, and after connection, also what are your continuity readings, any reason for leaving the 1mm kitchen lighting circuit, did you wire the drop downs to the wall lights, and switches.
if you think the cable to the living room light might be damaged, i would change that section. We await your response.



Its a metrel easy test i am getting >1000 IR on all tests on individual junction box connections i.e living room, landing lights sitting room and kitchen now i connect them all to mains feed (which is also >1000) and i am in the clear except when i connect the dining room lights , which on there own gives me >1000 but connected the whole circuit drops to around the 800's . I havnt done the kitchen because of access problems , even though it is comming up >1000 . I cant find a leak anywhere its a neutral earth problem , and as i said everything is new apart from kitchen, would the old 1mm cable to the kitchen be giving me hassle when loaded with the rest of the circuit??
Oh and all wiring has been changed 1.5 down to wall lights as well
 
mt MFT reads >99Mohms. that's good enough for me.
 
I am a little confused (but i am blonde) > 1000 on my meter means there is no connection , its like holding the leads in the air , yes
surely if i have a reading in the 800's i have a leakage somewhere? dunno i have never put down on my sheets anything other than >1000 am i being dumb can someone explain??
 
Are you winding us up, have a look in your regs book what does it say about min value that is Acceptable, as this is exissting instalation
all values you have quoted are fine, even for a new installation.

you just need to be a bit more confident in your work.
 

Reply to lighting circuit problem in the Australia area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
719
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
435
Hello, I added a 240v insta hot water heater at the kitchen sink. When the water heater is in use the lights in the adjacent dining room flicker...
Replies
1
Views
796
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
505
I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock