Hi guys, I am adding a lighting circuit to a Ring main 32 A. Can I just use a 6A MCB type B in a box on DIN rail to supply my lighting. I am using 1.5mm cable after the 6 A MCB.
Thanks for your advice!
 
As above, a FCU with a 5A fuse is the simplest option, just added as if it were a socket on the ring.

Or even as a spur. Though personally I dislike spurs due to the options for abuse (adding more later and not limited to 13A) as well as the higher risk of a conductor not being properly clamped if there are 3 (or more!) in an existing socket.
 
My issue is though in terms of short circuit by the lght, both the 6A mcb and the 32A mcb trigger. I would rther the lighting mcb to trigger only. shall I change into a rcbo o a different cb?
 
My issue is though in terms of short circuit by the lght, both the 6A mcb and the 32A mcb trigger. I would rther the lighting mcb to trigger only. shall I change into a rcbo o a different cb?
Feed the lighting through a FCU with a 5Amp cart fuse and, forget the 6A breaker and enclosure,
 
well , the 6 AMP mcb type B is overload and short circit protecting the lighting circuit. Only issue was to avoiding the 32 AMP ring mcb to trigger, hence the alternative CB . It needs calculating the arc current etc to determine the right mcb, but honestly I cannot bother as long as circuits are correctly sized.
 
You won't get much selectivity between MCBs. Check the manufacturer's tables for selectivity, or for Schneider this tool works (but only on Chrome web browser, it seems, which is crap):
https://hto.power.schneider-electri...f9fa18492b&client_id=cbt#/CheckDescrimination

Hager for the NBN series give 0.45kA limit (i.e. if your fault Zs is below 0.51 ohms then both fire).

Having said that, you won't get much selectivity with MCB - fuse either, though the Schneider tool seems a bit broken for that but from the current-time plots you are looking at 0.1kA limit (i.e. lower magnetic trip threshold of 3 * 32A for B-curve MCB)
 

Reply to Lighting circuit supplied from a 32A ring main socket. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock