Discuss Lighting fault on downlights in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Hi good morning.

I wonder if any one can help me.

Yesterday i replaced a fuseboard at a domestic property and added a few new circuits.

Eveything tested fine until i carried out a functional check on the lighting circuit. Which ever switch i turned on in any of the 5 rooms it would trip the RCD.

So as you do i started to test and investigate and fault find to why this is happening.
After a few hours of taking every downlight down and every switch off the wall. There didnt seem to be anything that wasnt wired correctly.

So i broke the installation down. Found where the 1st feed went to. Then wired the loop to the downlighs in that room straight on to my incoming feed trying to get them on permanently. AGAIN tripped the RCD.

I removed all of the LED GU10 lamps from that room and tried again. This time the circuit and the RCD stayed on. Tried to put one lamp in and AGAIN the RCD tripped.

Tried the same thing in all the other rooms and the same thing....without the lamps it stays on... put any lamp in it trips the RCD straight away.

I ran out of day late and by this time ideas. Has anyone had a similar problem and if so how do i go about rectifying the fault.
Any help would be gratefully appreciated.

Many thanks
Darren
 
Find it and rectify. Sorry, didn’t mean to sound sarcastic but that’s it in essence. Try putting all the lighting circuits on the same RCD or better can they be terminated into the same mcb? That all supposes the borrowed neutral is off a ‘like’ circuit. Good luck.
 
if it is a borrowed N on landing light, then it's usually only switching that one light on will trip RCD. as all other lights get their N from the correct N bar, and so there is no imbalance.
 
I've had a similar situation on a board change,
turned out to be an extra wall light installed on a downstairs lighting circuit, utilising a ' borrowed neutral' from the Ring final circuit immediately above the offending light, installed by a builder who said he knew what he was doing.......
It took me a day to find it after taking up most of the bedroom carpets and floorboards.
Good luck. You'll get a great sense of satisfaction when you do discover the fault.
 
Before doing a board change I always turn all the lights on in the house first before switching off the mains(also helps when testing IR during the board change).Then,after the board change,before switching on I test between the 2 neutral bars to make sure there's no continuity.If there is then I switch off the landing light first to see if it clears.It saves running around after you have switched on wondering why it isn't working.
 

Reply to Lighting fault on downlights in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
342
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
294
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock