a Bulgar is from Bulgaria, so a Meggar must me from Meggaria. think it's down in Dover.
 
UPDATE!

So I went back with my Meggar and found the issue!

Tested between the 2 switch lives at the switch and found a short (not picked up on my multimeter)

Started lifting floorboards to trace the cables and found a screw had just caught both switch lves in each t&e where they went through the joist!

These floorboards were lifted a week or so after I carried out the inspection and test!

The switch lives arcing together must be the cause of the LEDs burning out.

Sorted out the damage cables, tested and everything working bang on!

Appreciate all the advice and input given by everyone :)
 
now that's a good result. i assume the cables were just notched into the joists with no mechanical protection. well done for perseverance, and thanks for letting us know the outcome. and welcome to the world of finding awkward faults. :sunny:
 
now that's a good result. i assume the cables were just notched into the joists with no mechanical protection. well done for perseverance, and thanks for letting us know the outcome. and welcome to the world of finding awkward faults. :sunny:

The cables were drilled through the joist (not low enough down though) but also the nails were pretty long.

It's always nice to have a fault and find it! :)
 

Reply to lighting fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
617
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
891
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
686
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
294

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock