Discuss Live sockets in the UK Electrical Forum area at ElectriciansForums.net

G

gvelec

Hi all,

I'm new here, so please go easy :yes:. Would appreciate some assistance though.

I've just been around to my mums and go a little buzzing type shock from the toaster. I only had my electrical testing screwdriver with me as i'm miles away from home. The screws are indeed live for this socket as well as for a neighbouring socket. Verified that it is a ring from the DU, and have killed the circuit.

I've checked the earth connections to the sockets and they are fine. Any ideas on how i can test and fix this up in quick time with no equipment. I know that really should have been carrying my Kewteck multifunction :6:.

Thanks
 
you need to do a thorough test procedure. R1+R2 to start with. check also the main equipotential bonding to gas and water. check to see if you have a voltage N/E. , Ze, Zs, etc., etc.
 
I only had my electrical testing screwdriver with me.


frightening........


 
I know. Frightening! But travelled 150miles for the weekend. Didn't think I'd need my mf. I may well make a trip back tomorrow to pick it up. Can't leave it like this. Nor can I do a temp job until next week.

Thanks fellas
 
For what it's going to cost you in fuel it would probablu have been cheaper to post up the location and pay someone off here to come out with his test kit
 
Neon screwdrivers are the devils work and should be banned.

I take it there is no rcd, check they live conductors insulation isn't damaged and check the ze, could be too high for the fuse/mcb to trip
 
Neon screwdrivers are the devils work and should be banned.

I take it there is no rcd, check they live conductors insulation isn't damaged check the ze, could be too high for the fuse/mcb to trip
 

Reply to Live sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
277
Hi Recently my son complained that he was getting shocks from his laptop when plugged into the mains in his room. I checked the socket and the...
Replies
4
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock