That's looking more serious...…..earth in L2? Be Careful and get some advice if you've any doubts.I will have a look tomorrow I have a feeling that could Be it.. it’s a single poll switch but whoever done it has blue in common brown in l1 earth in l2 so I’m thinking is the earth mixed in a junction box because it’s t&e at switch and pvc pvc singles in ceiling
What’s the Ze? And the Zs?I am currently redoing a kitchen, (electrics) I tested voltage at lighting cable and form brown>blue-230ac
Brown>earth I got 25ac could anyone shed some light on this please
Give him a lift with it....if he knows his stuff, you'll learn.I’m gonna hand the job to a family friend (qualified) thanks anyways for your advice and help
that sets alarm bells ringing. looks like the cpc has been used as a live conductor in a 2 way set up.I will have a look tomorrow I have a feeling that could Be it.. it’s a single poll switch but whoever done it has blue in common brown in l1 earth in l2 so I’m thinking is the earth mixed in a junction box because it’s t&e at switch and pvc pvc singles in ceiling
Hi - As Marvo has said it's likely cpc not continuous. Do you have a loop tester?
if it is wired correctly, which i doubt, he should have 230V L-E.Not sure I agree with that .......... try turning off the other circuit breakers as it sounds like induced voltage to me
You shouldn't be getting 25V between Neutral and Earth either.Another option, is that the polarity is reversed.
Test a socket, see what readings you get.
Not sure I agree with that .......... try turning off the other circuit breakers as it sounds like induced voltage to me