Since leaving ELECSA I don't do that many notifiable works, normally if it's notifiable the customer is getting a lot of work done so just infrom Loacal Building Control, they come and do 1st fix inspection (look around for cables going straight up a.nd down). Once the job is complete I test as I would before, then pass the results to LABC.
I had a call today from building control, querying one of my test results sheets, well their electrical engineer querying it.
What are your thoughts.:rockon2:
I had a call today from building control, querying one of my test results sheets, well their electrical engineer querying it.
- The tails I wrote down was 16mm (well fair cop) and not 25mm, I'll change them not a problem.
- The BSEN number for the main switch Wylex board 100A main switch, which I've got as 90743, he claims is wrong.
- There is no mention of a split board on the schedule, as in cir 1-6 on RCD 1 and 7 - 12 on RCD 2
- And if it is a split board, why I have not used a 100mA RCD, well I used to pre 17th on a TT but all cables are buried less htan 50mm so it's got 2 30mA
- And how are all my circuits tripping out at 21mA 18ms (if tahts what my meter says thats what gets recorded)