Discuss Loop impedance and equipment cables in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many milliohms they need to include for equipment cables? I have been told "no", that the loop impedance is only up to the outlet. Now I am an R&D engineer who routinely uses 5 metre lengths of 4 mm^2 SWA to 32 A equipment - which is several tens of milliohms. I was told by the electricians who installed the wiring that this would be OK, but only because they had been kind enough to include a large factor of safety on top of what the regs require, which according to them is absolutely nothing......but surely loop impedance calcs should not only include Ze external to the building, but also reasonable lengths of equipment cable connected to the outlets too? And for my second question.....this is hypothetical because we actually have an on-site transformer....but there must be lot of people up and down the land working in tin sheds with TN-S earthing, and therefore a max Ze of 0.8 ohms. How on earth to they run 32 A or even 63 A supplies, when you cannot get safe disconnection times with 0.8 ohms? I feel there is something seriously wrong with my understanding here!
 
What actually matters in all these cases is the protective device, and whether enough fault current will flow to operate it quickly enough.
If you had a Ze of 0.8 ohms and a 32amp supply protected by a B32 breaker, then that leaves 0.3 ohms for the final circuit as the adjusted max loop impedance for a B32 breaker is 1.1 ohms.
230 / 1.1 = 209 amps which is enough to disconnect the supply within the 0.4 seconds for a TN earthed final circuit (there are graphs in the regs to show this)

If this isn't possible then using larger cables can help. In some circumstances (e.g. distribution circuits) considering different protective devices e.g. fuses can help.
Ultimately having exhausted everything else then RCD's can be used for fault protection and volt-drop becomes the most significant consideration.

Any circuit design should take into account how the supply will be used.
Does that help?
 

Reply to Loop impedance and equipment cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
591
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
751
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
I have a box powering three 3-phase motors off of one 240V single phase line, NEMA 10-30. In the picture you can see a wiring diagram. The...
Replies
8
Views
1K
Hi, I am currently studying to become an electrician and keep seeing this question (normally different values) and I am not sure how to work this...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock