Discuss Loop impedance measurement in the Electrical Engineering Chat area at ElectriciansForums.net

Reaction score
0
Hi, All

I have a megger LTW325 and fluke 1664FC to measure loop impedance by using high current mode. But both results are quite different. megger LTW325 is given a value 0.04ohms and fluke 1664fc is given a value 0.12 ohms. Means megger can give a current at 230V/0.04=5750A but fluke is only 230V/1.12=1916A.

Do you have any advices or expereince on this megger and fluke meter?
 
Something to discuss with the tech team of the manufacuturers as they would know details like that. They have been most helpful to me in the past when something of that nature has arisen.
 
Check you are using the probes supplied with the MFTs. The one I have (DiLOG) is "zeroed" at the factory for the supplied lead resistance and there is no provision for nulling that out (I asked them). It only takes 0.08 ohm to explain what you are seeing.

The other obvious things are clean connections on the probes and plugs, and if both meters are in-calibration (and have not be abused too much since they were checked).
 
Check you are using the probes supplied with the MFTs. The one I have (DiLOG) is "zeroed" at the factory for the supplied lead resistance and there is no provision for nulling that out (I asked them). It only takes 0.08 ohm to explain what you are seeing.

You sure about that? My 9110 uses one of the function keys for nulling - seems a bit odd that they'd make a meter on which replacement leads would cause errors. Conveniently, it holds that measurement until batteries are replaced.

Here's Rev2 manual for the 9118, which details lead zeroing around page 16.
 
Last edited:
I think I found it did not change the Zs value and asked them, but I can check tomorrow by deliberately using higher R leads and nulling them for low-ohm measurement.
 
I believe that once leads are nulled, they're taken into account for any resistance measurement until batteries are replaced. Lead nulling process is separate from any test, but IIRC it has to be carried out on continuity setting.
 
Doesn't make any sense that they'd be factory nulled as this would be a nightmare if leads need to be replaced. Also makes little sense that the meter would hold details for leads, but only apply them to one particular test.
You are 100% right, but that implies a sensible design where the low-R null value is incorporated in to the Zs computation.

The jury is still out...
 
I couldn't find the leads, and discovered it won't null out the ~1.1 ohms of my 50m extension lead, but I did find that enabling/disabling the lead zero for low-ohms made no observable difference to the L-N PFC measured (was seeing about 0.21 - 0.22 ohms in all cases)
 

Reply to Loop impedance measurement in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
727
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
606
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
887
I've managed to mainly fix a Megger 1502 MFT that was so far out of calibration it got laughed out of a tester day. I have high current loop. rcd...
Replies
11
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock