something like that. the higher current helps to get past tarnished contacts, that's why low current test often gives slightly different results. ( well that's my theory, anyway ).
It is one factor, but even then wiggling the probes/clips on low Z systems usually gets a slightly lower value.

More fundamentally the bigger the test current the larger the delta-V, and so it is easier to measure that and reject the wobbles on the supply that are usually there. For example, if test current is 20A then 0.3 ohms Zs is going to show a 6V change - easy to spot on 230V.

But if the test current is only 15mA to avoid tripping a RCD then you are trying to see a 4.5mV change in 230V or 0.002% which is why MFT take a long time to switch it on/off over and over so the supply noise gets averaged out but the disturbance reinforced.
 
Hi
I bought a holiday lodge last month and decided to test the circuits to see how they measured. The lodge itself is fed from a central point in the holiday village by a 16mm PVCSWA. The main earth wire terminates into a MET it looks to be a 10mm earth that is crimped onto the incoming earth, I cannot see what its crimped onto as the head the mains terminated into prevents this. Anyway I carried out the the normal tests on the circuits R1 R2 RN and these tested all within the expected parameters as an example the one of the rings measured R1.24 RN.24 R2 .39 and R1/R2 .25.
The other circuits all tested within expected parameters. The Ze measured .6, however when I powered up and did a Earth Fault loop impedance test the machine measured 23 ohms, this was repeated on all the sockets and the same measurement. Assistance required please as to the possible reason (s) for this.

Do you know the earthing arrangement, you say you cannot see what the earth is attached too so could it be a TT earth and the rod has resistance of around 23ohms
 
I dunno just know the uk tns is 0.8 max ,.we.dont have it

Could that be like a submain at 0.6 external loop, 16mm pvcswa sounds like it
 
Last edited:
It is one factor, but even then wiggling the probes/clips on low Z systems usually gets a slightly lower value.

More fundamentally the bigger the test current the larger the delta-V, and so it is easier to measure that and reject the wobbles on the supply that are usually there. For example, if test current is 20A then 0.3 ohms Zs is going to show a 6V change - easy to spot on 230V.

But if the test current is only 15mA to avoid tripping a RCD then you are trying to see a 4.5mV change in 230V or 0.002% which is why MFT take a long time to switch it on/off over and over so the supply noise gets averaged out but the disturbance reinforced.
Guys, al
Do you know the earthing arrangement, you say you cannot see what the earth is attached too so could it be a TT earth and the rod has resistance of around 23ohms
Hi There,
I measured the Ze and it was .6 so I would assume not a TT, I have asked the facility manager the question to confirm it.
 
I started again from the MET and retested Ze, that tested out at .2 ohms, don't ask me, I tested it numerous times and it didn't move from.6. The R1 & R2 values stayed the same as previously, I re-tested the Earth Fault Loop and it tested out .8 as I would have expected on one ring and 1.17 on the other, the cooker tested out at .11. I have no idea what happened here as there was no sign of the 23 ohms it tested out at when I posted the original plea for help.
Thanks to all for their inputs
 
No I didn’t, I have no explanation as to why this happened, it’s not the tester after the initial tests at the holiday lodge I tested my home address I knew the readings here and they tested as expected ??
 

Reply to Loop Impedance reading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
293
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
749
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
574
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
914

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock