Search the forum,

Discuss Loop testers in the UK Electrical Forum area at ElectriciansForums.net

a loop tester, or to be correct, an earth fault loop impedance meter , measures earth fault loop impedance. Zs, Ze etc. there are a few avo megger ones 2nd hand on ebay that will do the job as well as any other. be wary of the china/hong kong units, though.

look for a megger LT7. lovely bit of kit, and has no trip test facility.
 
Just inquisitive because I've never used one, was wondering why you'd need one. We can't all know everything, otherwise forums would be pointless.Still not sure what they do :19:
 
nope - live testing is banned in our place!!! I can live with that.

I'm now thinking a loop tester is just a megger, I used to use them a lot (and not for electrocuting each other either), just not for over ten year so am very rusty.
 
whats a "megger?"....if you mean an insulation resistance tester...then that aint a megger.....it aint a loop tester either.....take a look at section 9, 10, and 11 in the on site guide for test instruments and how to use them.....testing etc.....may be good to look in guidance note 3 as well Chris...
 
As you may know,Meggar was a term that encompassed anything and everything to do with insulation resistance testing
icon11.png


You owned a meggar,tested with a meggar and the circuit tested was meggered and if you wanted to borrow one,it was easier to say than insulation resistance tester
icon7.png
 
thanks for the help guys.

Fortunately for me we have a proper sparky on site so I always refer to him, however when he's not there people think that just because I'm the calibration engineer they can ask me to solve their problems. I have to tread very carefully.
 
theres a serious note here though as well.....a lot of the candidates undertaking the C&G 2391 are refering to an insulation resistance tester as a "megger"....and its costing em marks....likewise a low resistance ohmmeter isnt a "continuity tester"....their losing marks for incorrect terminology....
 
For an earth loop test in an industrial situation you’re going to need something very sensitive. Forget about doing it live unless you’re suicidal. From a 1000KVA 11/.44KV transformer you will have say two off 500mm² copper singles per phase and a single 500mm² for the neutral. From the incoming neutral I would run two 95mm² singles to the earth bar. If you fancy testing the prospective earth fault current at that point, you’re on your own, I’ll be legging it off up the road. All tests would be done “dead” using a Ductor. The earth nests would be checked by gradient testing. Remember the earth nest would be linked to the structure of the plant.
You will be looking for figures in the Micro Ohm range for all conductors, fault currents of say 50KA+.
I’ve only ever seen a local transformer fault in a training film by GEC (I think) it wasn’t pretty to see. I did see the aftermath of a local failure, a hole blown in ¼“ checker plate!
Obviously as you got out on the plant the prospective fault levels dropped, but the earth return path resistance didn’t due to the thousands of parallel paths. The first plants I worked on were all hot riveted together, no chance of a high resistance return path. It’s the reason for M&Q statutory testing we used a 70mm² wander lead and the Ductor to measure the return path.

Sorry I went in to “Rambling Sid Rumpole” mode
 
You may laugh Glen.
We had two trolleys with 200m of 70mm welding cable on each reeling drum. We were looking for readings in Micro/Mili ohms.
 
Last edited by a moderator:
There are plenty of descent manufacturers of Line-Earth looptesters, and you don’t have to be buying fluke. Those with the best marketing strategyseem to be the most popular, it doesn’t necessarily make them the betteroption. It’s a bit like Gucci or Armani! The flukes have been known to sufferblank screen and throw out a few error codes after a bit of rough treatment.

You can’t go wrong with the jap gear, nothing wrong with it.Look at Kewtech(Kyoritsu) for example, solid work horse you can kick around thestreet and it still works with values unchanged. Unit is also good, solid & reliable stuff. Afterall, most of the stuff we plug in these days causing the high leakage currents,and throwing up tripping issues in domestic RCD protected installs are loadedwith Japanese equipment. Their test instruments are no different in quality totheir TVs, Cars, and Motor bikes. You just got to ensure you grab the rightbrand.

There seems to be some tidy stuff on ebay lately. You may beable to save a few £££ as well. Good luck with that!
 
There are plenty of descent manufacturers of Line-Earth looptesters, and you don’t have to be buying fluke. Those with the best marketing strategyseem to be the most popular, it doesn’t necessarily make them the betteroption. It’s a bit like Gucci or Armani! The flukes have been known to sufferblank screen and throw out a few error codes after a bit of rough treatment.

You can’t go wrong with the jap gear, nothing wrong with it.Look at Kewtech(Kyoritsu) for example, solid work horse you can kick around thestreet and it still works with values unchanged. Unit is also good, solid & reliable stuff. Afterall, most of the stuff we plug in these days causing the high leakage currents,and throwing up tripping issues in domestic RCD protected installs are loadedwith Japanese equipment. Their test instruments are no different in quality totheir TVs, Cars, and Motor bikes. You just got to ensure you grab the rightbrand.

There seems to be some tidy stuff on ebay lately. You may beable to save a few £££ as well. Good luck with that!
well if kewtech were japanese ....its just that they arn`t.....made in a dedicated factory in china mate....this helps kewtech corporation keep the reigns on quality control...
 
You may laugh Glen.
We had two trolleys with 200m of 70mm welding cable on each reeling drum. We were looking for readings in Micro/Mili ohms.
trust me Tony...i wasn`t laughing at you mate...far from it.....of course i understand how such a CSA of cable would allow you to acheave such low readings.....
 

Reply to Loop testers in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock