I have been out to look at a system that is generating less than expected.
It has 21 x 190 watt Suntech modules. 9 on one string and 12 on the other.
The irradiance at the time of the test was 800 watts
Open circuit voltage was String 1 304 Volts and 4.47 Amps String 2 419 Volts and 4.49 Amps
The inverter is a Aurora Power On 3600 outd the display showed string 1 778 watts and string 2 1165 watts
I feel this was low for a 4 kW system.
Any thoughts? I feel the modules are ok ?
Thanks