I've just done an insulation resistance test between line and earth and got 0.0 Mohms for most circuits. Obviously this is an F1, but what I don't understand is why the CB doesn't trip. Is the answer that the resolution on my tester isn't high enough? So I could for example have 0.049Mohms and this resistance is high enough to prevent a significant earth fault loop path?
Thanks for any thoughts...
 
What circuits did you get the low readings on? which ones passed the test?
 
The best practice guide would code that as C2 for:
  • Insulation resistance of less than 1 MΩ between live conductors connected together and Earth
I could be the impedance is below the meter's resolution, as 50k would only dissipate around 1W so might not be apparent as a fault to the occupier (but could grow to be a fire hazard).

What about N to E resistance?

Or did you test L+N to E? If so you could have a load present and a N-E short which may not show up (definitely not if no RCD, sometimes as spurious trip if RCD).
 
I've just done an insulation resistance test between line and earth and got 0.0 Mohms for most circuits. Obviously this is an F1, but what I don't understand is why the CB doesn't trip. Is the answer that the resolution on my tester isn't high enough? So I could for example have 0.049Mohms and this resistance is high enough to prevent a significant earth fault loop path?
Thanks for any thoughts...
Was it the same at 250V and 500V? If it's happening on several circuits only at 500V then could there be surge protection somewhere?
 
I've just done an insulation resistance test between line and earth and got 0.0 Mohms for most circuits. Obviously this is an F1, but what I don't understand is why the CB doesn't trip. Is the answer that the resolution on my tester isn't high enough? So I could for example have 0.049Mohms and this resistance is high enough to prevent a significant earth fault loop path?
Thanks for any thoughts...
You need to disconnect the earths and neutrals out of the common bar and then test individually swnds like you have tested across the common bar. Surely you done this?
[automerge]1600810308[/automerge]
You need to disconnect the earths and neutrals out of the common bar and then test individually swnds like you have tested across the common bar. Surely you done this?
You’re not diy are you?
 
What circuits did you get the low readings on? which ones passed the test?
Cooker and water heater passed, upstairs and downstairs power and lighting failed.
[automerge]1600837183[/automerge]
The best practice guide would code that as C2 for:
  • Insulation resistance of less than 1 MΩ between live conductors connected together and Earth
I could be the impedance is below the meter's resolution, as 50k would only dissipate around 1W so might not be apparent as a fault to the occupier (but could grow to be a fire hazard).

What about N to E resistance?

Or did you test L+N to E? If so you could have a load present and a N-E short which may not show up (definitely not if no RCD, sometimes as spurious trip if RCD).
The best practice guide would code that as C2 for:
  • Insulation resistance of less than 1 MΩ between live conductors connected together and Earth
I could be the impedance is below the meter's resolution, as 50k would only dissipate around 1W so might not be apparent as a fault to the occupier (but could grow to be a fire hazard).

This is what I was getting at, thanks.
[automerge]1600837514[/automerge]
What about N to E resistance?

Or did you test L+N to E? If so you could have a load present and a N-E short which may not show up (definitely not if no RCD, sometimes as spurious trip if RCD).

L to E were the problems, L to N and N to E were fine.
 
Last edited:
Any evidence of rodent damage?

I have seen a circuit trip the MCB then reset OK, but IR test showed high tens of k ohm so clearly not good. Was the result of mice in a home.

I guess if they eat the N insulation it might still have enough of a gap to clear 500V when tested later, but if chewing live and they go bang! it leaves some carbonised mouse around the place :(
 

Reply to Low insulation resistance and tripping circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
643
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
1
Views
308
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock