Discuss Low IR readings on lighting circuit - 0.654 Mohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I have spent quite a bit of time today trying to understand why I am only getting 0.654Mohms on the upstairs lighting between Live and neutral (at 250V)!!!

L-N 0.654 Mohms
N-E 25.11 Mohms
L-E 24.7 Mohms

I get almost the same when measured at 500V (cant remember exactly but about 0.6Mohms)
I get 105.5 Mohms when I measure between L+N combined and E.
Upstairs contains lights/extractor fans/shaver units

I have looked in every junction box in the loft and every light and switch and dont know what else to do.

Perhaps break the circuit down is the next step?

I just need 0.346 Mohms and then I will be a happy man! :sad:
 
possibility of something still connected. aerial amp in attic? neons? as long as yout L/N - E reading is acceptable, worry not.
 
Yeah, it's a wee bit low, check the bathroom fittings and fan for damp to start with. If not then just split the circuit into sections and track it down. Even getting it to a Meg is questionable, you don't know how stable the readings going to be so I'd be looking for considerably better readings than that.

*edit* got beaten to the post but I like Tel's idea as well.
 
I have spent quite a bit of time today trying to understand why I am only getting 0.654Mohms on the upstairs lighting between Live and neutral (at 250V)!!!

L-N 0.654 Mohms
N-E 25.11 Mohms
L-E 24.7 Mohms

I get almost the same when measured at 500V (cant remember exactly but about 0.6Mohms)
I get 105.5 Mohms when I measure between L+N combined and E.
Upstairs contains lights/extractor fans/shaver units

I have looked in every junction box in the loft and every light and switch and dont know what else to do.

Perhaps break the circuit down is the next step?

I just need 0.346 Mohms and then I will be a happy man! :sad:

Surely you need 1.346??

Did you disconnect the shaver point?

As Tel says link L&N to E then move on!
 
possibility of something still connected. aerial amp in attic? neons? as long as yout L/N - E reading is acceptable, worry not.

As above, something still connected and it will be the last place you look. If the test is ok when you connect L & N together, then all good.

Cheers Guys,

Yes, when I read similar threads they said the same. Why does it make it ok if you have a good Live/neutral combined IR reading? The IR between L and N is still poor and could mean a problem? (Although I'm guessing it doesn't as otherwise you guys wouldn't have said it!). Why does the good reading between L+N combined and E show that it is an appliance still not accounted for and not a wiring/damp/poor insulation problem?
 
It could still be a damp problem but the higher IR L+N combined to earth makes it more likely to be a small load still connected....although it would be a very small load.
 
it's all a matter of experience. if you get a lowish reading L-N , and all cables and accessories appear in good order, then it's a judgement call as to whether you accept it or investigate further.
 
It could still be a damp problem but the higher IR L+N combined to earth makes it more likely to be a small load still connected....although it would be a very small load.

Thanks Marvo,

So would you investigate until you found the cause or like Tel and others have said move on?

Plus, on the MWC how would I document this?
 
it's all a matter of experience. if you get a lowish reading L-N , and all cables and accessories appear in good order, then it's a judgement call as to whether you accept it or investigate further.

In that case I need to investigate further as I dont have the instinct to know whether it is acceptable!

I was going to have a day off tomorrow and perhaps have a pint at the local but now I will hunt for ohms!
 
Thanks Marvo,

So would you investigate until you found the cause or like Tel and others have said move on?

Plus, on the MWC how would I document this?

I don't know if it's within the regs or not and I'm not sure how you document it on a minor works, in South Africa we work to different standards and paperwork. Just over half a meg at 250v is a bit low for my tastes, I'd investigate to be honest. It's low enough to be a definite problem and it might come back and bite you later if you don't improve the reading.
 
Did you disconnect the fan/shaver point before testing? Are there LED downlights on the circuit (could be a snubber in there somewhere)? Trying to make sense though I am a tad tipsy!
 
Have had a faulty fittings can cause issues. I installed a brand new ring with all new fittings but got a reading of 168Mohms @ 250 volts. was all down to a one faulty socket.
changed and strait away got >2000Mohms @ 500v
 
Last edited by a moderator:
As said, it is probably a load you haven't disconnected but it does no harm chasing it down just in case.

Just a hint though, if it is low at 250V it really isn't a good idea to test at 500V or when you do find that load you missed you might just find yourself replacing it free of charge after it has objected to 500V up its chuff.... :(
 
Cheers Guys,

Yes, when I read similar threads they said the same. Why does it make it ok if you have a good Live/neutral combined IR reading? The IR between L and N is still poor and could mean a problem? (Although I'm guessing it doesn't as otherwise you guys wouldn't have said it!). Why does the good reading between L+N combined and E show that it is an appliance still not accounted for and not a wiring/damp/poor insulation problem?

If the low reading was caused by damp, I would expect to find L-E/N-E readings to be of very similar values as the L-N readings as I'd expect damp to affect all conductors.
I'd say, by your readings that you have load connected somewhere, reconnect the circuit, power up and put clamp meter on it, to see if there is any load being drawn, this may help you identify what's on there.
 

Reply to Low IR readings on lighting circuit - 0.654 Mohms in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
646
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
629
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
472
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
644
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock