Hi Everyone

apologies for not posting in the DIY section but it's locked and not allowing new posts.

We've seen IP65 rated small decking LED lights at Wickes which we thought to use in the bathroom, set into the wall (skirting level). We hope to fit them under a wall hung sink and toilet and possibly around the bath (bath side and end panel are tiled). First things first, is this safe? They are exterior rated, pressure jet rated and IP65.

If safe, the lights come ready to fit onto a 3 pin plug, which plugs into the ring main. We want them on the upstairs lighting circuit (circuit has RCD protection (split load consumer unit)) operated by a normal light switch in the wall. Is this safe/allowed?

Thanks a lot for your help!
:D
 
does the kit come with the driver/s built in the plug/s? if so then you must plug them into a socket.
 
Hi Everyone

apologies for not posting in the DIY section but it's locked and not allowing new posts.

We've seen IP65 rated small decking LED lights at Wickes which we thought to use in the bathroom, set into the wall (skirting level). We hope to fit them under a wall hung sink and toilet and possibly around the bath (bath side and end panel are tiled). First things first, is this safe? They are exterior rated, pressure jet rated and IP65.

If safe, the lights come ready to fit onto a 3 pin plug, which plugs into the ring main. We want them on the upstairs lighting circuit (circuit has RCD protection (split load consumer unit)) operated by a normal light switch in the wall. Is this safe/allowed?

Thanks a lot for your help!
:D
I wouldn't be rushing to fit those in a bathroom!
 
Not that it is likely to matter in your bathroom but IP65 is not pressure jet rated.
 
Hi

I thought IP65 would make them ok for bathroom use. The pressure testing was just written on the box. You're right that under a toilet or sink it's a non issue! :wink_smile:

Would it be ok to run them off the lighting circuit and off a light switch rather than the plug? Should I (or not bother) with a fused spur too?

Thanks for your help!
 
Sorry just saw previous posts (iPhone! Grrr). The driver is supplied connected to a plug with a wire but they are separate. Can u recommend suitable lights please if these really shouldn't be used?


Thanks!
 

Reply to Low level LEDs in bathroom - please help in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi All! I’m a hobbyist, but fairly skilled. I recently wired up a high end theater in my home, various new circuits, light fixtures, switches...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi there everyone. Kevin here. Hoping I can ask a question please. Home DIY'er with no official electrical training. Extent of diy electrics...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock