Discuss Main Bonding for incoming plastic pipe in the DIY Electrical Advice area at ElectriciansForums.net

D

Deleted member 112675

Hello All

Noticed the existing bonding for the cold water supply is only 4mm. The supply pipe out of the ground is clearly a plastic pipe. It joins a brass stopcock under the kitchen sink cabinet and the rest of the plumbing in the house is in copper. I'm worried I need 10mm bonding and will have to find a route for the cable.

For example, this company below says
" If the incoming pipes are made of plastic, but the pipes within the electrical installation are made of metal, the main bonding must be carried out. "

Are they right and will my forthcoming EICR fail because of it ?
 
Appreciate your comments on that website - I thought the same.

I guess a plastic pipe isn't conductive even though this one is extraneous. I didn't know whether or not it needs main bonding and I still don't know. It might have been nice to know whether or not I'm likely to need any additional cable running from the vicinity of the CU to the extraneous insulating part before the kitchen is finished and the EICR is done.
 
Appreciate your comments on that website - I thought the same.

I guess a plastic pipe isn't conductive even though this one is extraneous. I didn't know whether or not it needs main bonding and I still don't know. It might have been nice to know whether or not I'm likely to need any additional cable running from the vicinity of the CU to the extraneous insulating part before the kitchen is finished and the EICR is done.
Anyone else have a view? I don't see why you would need to test this aspect as the pipe as it enters the property is clearly plastic and not an extraneous conductive part? It has existing 4mm bonding back to the met but does it need upgrading (or even removing?)
 
Anyone else have a view? I don't see why you would need to test this aspect as the pipe as it enters the property is clearly plastic and not an extraneous conductive part? It has existing 4mm bonding back to the met but does it need upgrading (or even removing?)
Can nobody give me the answer because everyone has a different opinion on it? Maybe its just a boring subject ?!

JW (John Ward ) from youtube seems to imply its not necessary but that doesn't help me if I get an inspect and test and the guy I've given several hundred pounds to already says it needs a 10mm bonding? Maybe I could just ask whoever I'm planning to use (hopefully from this forum) whether they would class it as c2 before they take the job and start?
 
I gave you an answer. Whoever does your EICR will test if it’s extraneous
[automerge]1601493913[/automerge]
If it’s plastic coming in then it will likely not need bonding, but may if the tests indicate it does.
 
Hi - clearly your incoming water supply does not require bonding as it’s plastic. However we can’t say if the other metal pipework requires bonding without testing it, sorry.
 
  • Like
Reactions: DPG

Reply to Main Bonding for incoming plastic pipe in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
599
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
Replies
8
Views
6K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K
Hi sorry very long one. Please hop to bottom paragraph for short version. I’m just about to refurb bathroom in my 1986 house but bonding always...
Replies
36
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock