Discuss Main bonding to metal container inside warehouse in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Seen many answers on this but still not sure on a definite answer.
Power installed inside metal container, the units inside a warehouse, the supply to the warehouse 200amp TNCS
The power points are Rcbo protected,so is the lighting inside the container, 16/6 amp respectively.
Will this-require Main bonding protective conductors, the unit sits on concrete floor
 
My view...

It's almost certainly insulated from real earth enough to not be deemed extraneous, as dry concrete is a decent insulator. You could cover yourself by doing IR test from the shell to MET and check that it's resistance to MET is miles higher than 22,000 ohms. I'd be amazed if it wasn't. Therefore not extraneous, doesn't require bonding.

The other matter is whether due to the equipment and the way it's fitted the shell could become an exposed conductive part under fault conditions and require earthing. I think I'd take the view that with functional ADS (and additional RCD protection) it's safe enough.
(Also in back of mind is that we would want a very good reason to earth it and make the entire shell live in (unlikely) OpenPen conditions. )
So obviously without seeing it, I'd err on saying "no".

I'll now get the popcorn and see what others think....
 

Reply to Main bonding to metal container inside warehouse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi guys I have been tasked with upgrading some old rewireable fuseboards for a food warehouse that runs continually 24/7. I was asked to do an...
Replies
10
Views
2K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock