Discuss Main breaker trip in the UK Electrical Forum area at ElectriciansForums.net

tank

-
Reaction score
16
Hi guys, why might a fault on a final circuit in an apartment trip the dp c63 submain circuit breaker in the plantroom but not any mcbs on the consumer unit in the apartment?
 
A kitchen fitter did something which took out the breaker in the plantroom but not any mcbs on the consumer unit in the apartment. I insulation resistance tested the submain and it was fine.
 
If the fault current was high enough to achieve instantaneous tripping on both devices, it's a coin flip which one goes first.

MCBs are notoriously poor for achieving effective discrimination/selectivity and are often installed in-line as a product of poor design and nothing more.
 
same thing with this 3A fuse for bathroom fans crap, when they are on a 6A MCB protected circuit. the MCB is likely to trip instead of (or as well as) the 3A fuse.
 
Typically you need the fancier electronic type of MCCB that allows a short delay before firing (at least up to its own high instant magnetic trigger point) to allow any chance of good selectivity - i.e. if a down stream fault occurs then it only trips the downstream breaker.

MCBs in series rarely have much selectivity. Often it is barely more than the instantaneous trip of the upstream one, so if you have a 63A C-curve breaker that is 315-630A. Hence if the fault impedance is below 0.73-0.36 ohms then the upstream one probably goes as well (since it is already underway to trigger before the downstream MCB contacts have opened).

Or you use a fuse up-stream. Then you typically need a far bigger PFC to blow it, and might even get total selectivity.
 

Reply to Main breaker trip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
474
Could the sun’s heat on a caravan mains supply cable cause the fuse/circuit breaker at the meter box/supply end to trip?
Replies
20
Views
1K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
819
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
825
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
854

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock