Search the forum,

Discuss Main fuse protection in the UK Electrical Forum area at ElectriciansForums.net

Even with an intermediate fuse between the main fuse and consumer unit there is no guarantee one will blow before the other
With BS88 series fuses you get selectivity at ratios of 1.6:1 or more. So if the incomer is a 100A fuse then next one has to be 63A (or less) to achieve selectivity.

If you mix fuses and MCB (or MCCB) down stream it gets far more complicated and typically you get 3 regions:
  • Current below MCB rating = all happy
  • Above MCB rating, but fault let-through (I2t) less than pre-arcing of the fuse = MCB trips, fuse survives.
  • Fault current such that fuse pre-arcing I2t exceeded and both fuse and MCB go.
 
I have a 80 amp RCD after the meter fitted by an electrician.
Unfortunately the type used does not allow for differentiation from other RCD in the house.

my CU is old wylex so at best if one of my house RCDs triggers so does my main RCD but at least I can withdraw the fuses from the CU , reset the RCD and install the fuses one at a time to identify the circuit at fault.
 
I have a 80 amp RCD after the meter fitted by an electrician.
Unfortunately the type used does not allow for differentiation from other RCD in the house.

my CU is old wylex so at best if one of my house RCDs triggers so does my main RCD but at least I can withdraw the fuses from the CU , reset the RCD and install the fuses one at a time to identify the circuit at fault.
The rcd won’t trip at 80A, would need to be an rcbo.
Cant you remove that one if there’s rcd’s in the CU?
 
Hi all. Reassuring that this is an uncommon issue. Here's my use case. I have 2 CUs with total 180A on their main switches on a 100A DNO fuse. I load shift as much as I can into a 6 hour window on Intelligent Octopus.
That means 10kw of storage heaters, 7kw car charger, 3kw immersion, 3kw battery charger. 23kw already. Add to that the washing machine, tumble dryer, dishwasher, and then heaven forbid someone makes toast at night!
So in deep winter I could run somewhat over 24kw for several hours. I've not done this yet. But this, surely, would blow the fuse, right?
Thanks in advance
 
24kw is barely over 100a, it'll take another 20% or more for brief periods. I doubt very much you ever get anywhere near 100a. Dont forget your storage heaters only operate at night.
A 100a service head will inevitably show heat damage if it has been subjected to maximum loads constanty for long periods , they are not designed for this. I maintain a large property with extensive electric UFH, a large electric AGA, electric water heating, and a kitchen with every coceivable appliance. It has been running on a 60a head for decades.
 
Thanks for that. Yes the point is that everything I listed is on during the same 6h cheap electricity window. So I think I risk running over 100A for some hours at a time.
I suppose I need to look at pricing up 3 phase...
 
A cheaper option than have a 3ph supply installed might be installing a load shedding relay that will isolate heavy loads if total gets near 100A.
 

Reply to Main fuse protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Shop with a 100A main fuse LED lights few amps max, cash tills, cash machine, roller shutter, auto door, nothing pulling much power but...
Replies
6
Views
617
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
324
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock