we have a mains supply 400A from a switch room which is fed from a switch fuse to a old Bill red spot board which is approx 80M away,we are removing the fuse board and installing a bus bar chamber in its place,do we need to install another switch fuse isolator below the bus bar chamber or is the one in the switch room adequate as long as we label the bus bar where to isolate
martin
 
Provided the switch-fuse disconnector can be locked off in the switch room then it should be okay. Personally I would install an Eaton chamber which allows the mounting of a Glasgow switch-fuse with a linking kit to connect to the chamber.
 
The last Glasgow switch I saw was made decades ago (in Glasgow)!

More recently folk on here suggested the Square D option so I got a SQB1003K (100A TPN) for a new project and will be getting another two to complete it hopefully soon. They seem well made, are cheaper than the (seemingly identical) Merlin model, and had two features I really like:
  • Double switched so both ends of fuses are fully isolated (i.e. you can use it top or bottom fed, or in our case with a potential back-feed of leakage current from several UPS).
  • The safety covers over the terminals go to the box edges, so if changing a fuse you don't risk dropping it or a nut, etc, and them ending up in your busbar chamber.
Still waiting for our sparky to de-furlough to get it fitted at the site, but that aspect is not really under our control.
[automerge]1589619084[/automerge]
One thing is they are quite compact (rather like the Glasgow ones) so if you have big SWA then you are more likely to need a spreader box than some of the others that are in bigger boxes to begin with.
 
Last edited:
The last place I worked at was all Glasgow / MEM fused stuff put in early 70s, lasted without a hint of trouble until it was rewired around a decade ago and they went Square D boards.

Unfortunately a few folk have reported the quality of the MEM / Glasgow stuff has suffered in recent years, but I have no first-hand experience to say.
 
More recently folk on here suggested the Square D option so I got a SQB1003K (100A TPN) for a new project and will be getting another two to complete it hopefully soon. They seem well made, are cheaper than the (seemingly identical) Merlin model, and had two features I really like:
  • Double switched so both ends of fuses are fully isolated (i.e. you can use it top or bottom fed, or in our case with a potential back-feed of leakage current from several UPS).
  • The safety covers over the terminals go to the box edges, so if changing a fuse you don't risk dropping it or a nut, etc, and them ending up in your busbar chamber.

Any fused switch will withdraw the fuse completely, that's the difference from a switch-fuse.

Yes the Square D and Merlin Gerin are identical apart from the paint colour and the price, both brands are part of the schneider group now.
The reason given by the schneider rep for why the Merlin Gerin is more expensive was 'because specifiers want MG so we can charge more for it'

The same goes for Acti 9 RCBO's versus IKQ RCBO's, exactly the same device but with different screen printing (and a busbar clip)
 
Any fused switch will withdraw the fuse completely, that's the difference from a switch-fuse.
That was what I assumed, but it seems that terminology is not used consistently. Take Hager, for example, on page 86 of the catalogue here:

They define "Switch Disconnector Fuse" as the double-break style, but "Fuse Switch Disconnector" as the single break of moving-fuse type. Of course when you look at their range on page 40 they are called "Fuse Combination Switches " which is a term not mentioned anywhere in the technical details page! Helpful, not...
 

Reply to Mains isolation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening, I've been asked to install a supply to a sprinkler system in a new installation that must be separate to the building electrical...
Replies
2
Views
607
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
889
Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this...
Replies
15
Views
1K
Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
726
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock