Discuss Mains operated interconnected smoke alarm in the UK Electrical Forum area at ElectriciansForums.net

Neptune

DIY
Reaction score
24
I fitted these into my own house a few years ago when everything was ripped open and hence, am familiar with the process.
However, on this occasion I need to fit these into a property that I let out and I don't have access to the ceiling void on ground floor.

I was thinking about using trunking and wanted to check on what type of trunking is neat and recommended for this purpose. Also, how will this merge into the existing light pendant (standard light pendant hanging from the ceiling).

Finally, I assume that I will need to trunk to the switch and not light if that's where the permanent live is. If this is the case, how will the trunking merge into the existing light switch?

Never had to use trunking before. Thanks in advance.
 
First check there isn’t a live and neutral at the light... older houses, this is where it was. Neutrals at switches is a fairly new thing.

from the light, you only need a live, neutral and earth to first smoke, then a 3 core and earth in a daisy chain to each other detector in turn. Live neutral earth and interconnecting cable.

some manufacturers offer 10 yr lithium detectors with radio signal interlink, for when you don’t want to disturb decoration,
Or mains with a radio module. Or the house can be a mix of wired and wireless...
 
One thing you will need to be careful of is the requirement for protection against premature collapse in the recent regulations.

Plastic trunking along a ceiling or high up on a wall could be liable to collapse during a fire, and cause potential risks to the tenants getting out, or fire fighters who are dealing with the situation.

There are metal clips available that fit inside plastic trunking to support the cabling in the event of the worst. I believe best practise is to fix them not with plastic rawl plugs, but with entirely metal fittings - you may be able to get metal screws into the joists for example.

In a standard hallway you may only need one or two of the clips on a run of trunking, with other fixings being normal rawl plugs if necessary
 
Thanks for all the responses. Really appreciate it.
How about the trunking detail when it connects to the light pendant?

Also, is there a certain type/profile of trunking you recommend? I noted the point re. metal clips.
 
You can get ceiling rose adapters for mini trunking it will drop the rose a bit but gives a neat solution.
As for internal metal fixings most are designed for 25 Ă— 16 and upwards but if using 16 Ă— 16 there are these although I have never tried them.
 
Last edited:
TBF, they can all be battery and radio-linked, at least the Aico ones can. I generally used to install the hall smoke as a wired, from a light, with a 10 year battery, and the rest just 10 year battery, radio linked. No mains wired for me now...why bother?
Unless your local BC have other ideas...
Better to have something that works, IMHO.
 
TBF, they can all be battery and radio-linked, at least the Aico ones can. I generally used to install the hall smoke as a wired, from a light, with a 10 year battery, and the rest just 10 year battery, radio linked. No mains wired for me now...why bother?
Unless your local BC have other ideas...
Better to have something that works, IMHO.
This would be a Grade F system according to BS5839:6. You're quite correct in saying that some local building control/councils will not accept anything other than Grade D (mains interlinked).

However it should be ok in the private rented sector, as the actual legislation from October 2015 doesn't require mains OR interlinking, just smoke alarms on each floor.
 
Thanks for all the responses. I really appreciate it.
My Local Authority has expressly stated that I need mains powered and cable interconnected smoke alarms. they do not approve the wireless system.

Once, I have confirmed the presence of permanent live in the ceiling rose I will use the trunking and clips mentioned to complete this task.

I also thought there was a "heat resistant" type 3 core and earth cable. Perhaps I should use that for the interconnect?

Thanks again
 

Reply to Mains operated interconnected smoke alarm in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
316
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
I'm about to start first fixing this fire alarm in the industrial unit we are wiring, at the moment its totally empty and eventually will have a...
Replies
5
Views
857
Had a floorboard up recently following a water leak. While there, thought I would connect in a stair light, which previously was switched...
Replies
2
Views
746
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock